Allan, I think most gennies bond the neutral to the chassis so the circuit breakers on the gennie will trip in the event of a ground fault. If the neutrals weren't bonded and the breakers didn't trip to clear it, there would be a shock hazard on the chassis in the event of a fault. Not sure what you mean by suggesting to disconnect the grounding conductor on the extension cord. If there's a ground fault in the coffee maker, that might leave any metal parts of the appliance energized and thus be an extreme shock hazard. Better to investigate the gennie for a ground to neutral bond as well as the inverter BOS and rewire so the is only one neutral to gound bond in the entire system, as required by code. Apologies in advance if I have misunderstood your suggestion. Your posts are invariably right on.
Dick Ratico Solarwind Electric Jeremy, Outback may be right on, and it's worth checking. Most portable gennies internally bond neutral to chassis, because they expect that no typical homeowner will ground the chassis. (Inverter-generators are a noteworthy exception to this.) Most inverter systems also have a neutral-ground bond, if done to Code. Whe plugged into the gennie, there's thus an inherent ground loop. Try disconnecting the grounding conductor on the extension cord. Allan Allan Sindelar [email protected] NABCEP Certified Photovoltaic Installer NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder and Chief Technology Officer Positive Energy, Inc. 3209 Richards Lane (note new address) Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com On 6/7/2013 9:10 AM, All Solar, Inc. wrote: I found out that the appliance will work fine from an extension cord with a portable generator. The appliance will not even work however when the backup gen is running and transfering through the inverters. Outback T.S. suggested to check the Neutral to ground bond so that is the next step. Also tried to set the Power Save levels the same (stacked pair) Jeremy All Solar ----- Original Message ----- From: Exeltech To: RE-wrenches Sent: Wednesday, April 17, 2013 1:51 PM Subject: Re: [RE-wrenches] Outback wave form Wrenches, While the addition of a capacitor may resolve issues associated with various inverter/appliance/motor combinations, please make sure the capacitor(s) get switched OUT of the circuit (disconnected) when the load itself is disconnected. Failure to do so could under some circumstances cause the inverter control-loop circuitry to go unstable, leading to unpredictable inverter operation, and possible damage/failure in the power system. Disconnecting the capacitor with the load alleviate this possibility. Regards to all... Dan Lepinski --- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems <[email protected]> wrote: From: Larry Crutcher, Starlight Solar Power Systems <[email protected]> Subject: Re: [RE-wrenches] Outback wave form To: "RE-wrenches" <[email protected]> Date: Wednesday, April 17, 2013, 2:09 PM We experience issues like this from time to time. PF seems to be the culprit. Have you measured it or looked at the waveform yet? How an inverter deals with PF seems to vary broadly. For example, the Splendide XC2100 washer/dryer will not work on a Magnum Energy and a few other sine wave inverters. However, it will run on a low cost GoPower or Samlex sine wave inverter. Below is a scope trace of voltage/current of the Magnum inverter & Splendide washer. Upper trace is voltage By adding a 50uF run capacitor inline, it somewhat tames the current phase and the sine wave so the Magnum can operate the washer. (Special thanks to Al for the discovery and photos) Larry Crutcher Starlight Solar Power Systems On Apr 16, 2013, at 9:46 AM, All Solar <[email protected]> wrote: Have a client with a new coffee maker that will not run from their new dual outback setup. Has anyone heard of this lately. We have had no problems with appliances and sine wave inverters. What to look for? Sent from Jeremy's IPhone. Sorry for typos and shorthand! _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org -----Inline Attachment Follows----- _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org