This seems like another well meaning but slightly awkward code
requirement. I think it would be sufficient to list the nominal battery
voltage (very important to know) and then the actual variation in
voltage is not going to be too hard to comprehend.
Knowing array Voc is also very important. If you think you have a 12 v
based battery system, but the array is actually at 480 Voc, you need to
know that, before taking any covers off.
Code requirements aside, I think we need to list:
Array Voc
Battery Nominal Voltage
AC voltages
That should be on the outside of every J box with connections inside, so
you know how to set your meter. If there's DC, and you're testing for
AC in a box, you might think power is off. My handy voltage sniffer
only senses AC for instance, so modern battery based PV systems can get
dangerous with high voltage DC arrays, especially if you're trouble
shooting a DIY system. I've seen wires fed by three different sources,
and gotten shocked trying to remove the 2nd source.
On code requirements like this, I move closer to the spirit of the law,
which is to keep everybody safe. The inspectors usually agree, but
you'll always have an AHJ that wants something different.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 6/11/2013 9:33 AM, jay peltz wrote:
HI All,
I mean as its worded, it would also be 240vac?
jay
peltz power
On Jun 11, 2013, at 7:30 AM, [email protected]
<mailto:[email protected]> wrote:
Hi Bob,
I would rather it be worded "maximum normal operating voltage".
Maximum operating voltage would be the recommended BULK voltage for
the battery type being utilized.
Equalization is a maintenance procedure, which is why it calls for
separate listing.
It must also include polarity of grounded conductor.
Eric
_____________________________________________________________________________________
*
Eric Bentsen* | *Schneider Electric ** | Solar Business* |
*UNITED STATES* | *Technical Support Representative* *
Phone:* +(650) 351-8237 ext. 001# | *
Email:* [email protected]_
<mailto:[email protected]> |
*Site:*_www.schneider-electric.com/solar_
<http://www.schneider-electric.com/solar> | *Address:* 250 South
Vasco Rd., Livermore, CA 94551
_
_<Mail Attachment.jpeg> <x-msg://179/www.schneider-electric.com/solar>
*** Please consider the environment before printing this e-mail
From: "Bob Clark" <[email protected] <mailto:[email protected]>>
To: "'RE-Wrenches'" <[email protected]
<mailto:[email protected]>>
Date: 06/10/2013 08:08 PM
Subject: [RE-wrenches] NEC 690.55 - "maximum operating voltage"
Sent by: [email protected]
<mailto:[email protected]>
------------------------------------------------------------------------
RE_Wrenches:
Can someone tell me what is being referred to in NEC 690.55 when it
says "Photovoltaic power systems employing energy storage shall also
be marked with the "maximum operating voltage, . . ." ?
We have an off-grid system which employs energy storage [i.e.;
batteries]; so I need to know what exactly is referred to when this
section mentions "maximum operating voltage" so I can put it on a sign.
*Bob Clark*
*/SolarWind Energy Systems, LLC/*
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org