The Outback rep got me some good info, and I'm liking the Radian with
the Remote controlled breaker to control the GT inverter when the grid
is out. I've heard of quite a few problems related to the Sunny Island
frequency controlled system.
My question is can off grid inverters like the Magnum be AC coupled?
I'm trying to get the price down, and still handle the 240 vac input
from the GT inverter.
I penciled out the Radian and I was topping $10k before installation.
This customer is hoping for a solution under $10k, and closer to $5k if
possible. I think an elegant lower cost solution for Grid tie with
battery back up is in order. A Radian Lite?
For backup, it could even be mod sine, as it wouldn't be much worse than
generator power or the average UPS setup.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 7/30/2013 2:59 PM, Ray Walters wrote:
Hi All;
I know AC coupled systems have been covered before, but I have a new
issue: positive grounding. A customer with an existing 8kw Sunpower
system wants to add backup. He was put off by the high cost the
Sunny Island, so I was steering him towards a single Outback VFX
coupled to just one of his 3 inverters. The issue is how will the VFX
work with positive grounded inverters. I'm assuming that since the
two inverters will only be connected by AC, that the positive vs
negative grounding of their separate DC systems will not matter. Any
experience with this particular scenario: Sunpower system AC coupled
to an Outback?
Also, would I even need a GVFX, since the inverter would only be used
during outages (which might allow a generator to be used later as
well) A VFX should still AC couple to the GT inverter during an
outage, right?
Thanks as always,
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org