We have installed one dual Radian system. We looked at the prewired 
distribution boxes from OutBack (MidNite's wasn't out yet at that time) but 
they had no bypass solution for two inverters. We ended up using an external 
100 A, 2 pole, double throw safety switch for an AC bypass from the generator 
feed, a little spendy but the only thing we could come up with. The newer 
MidNite E-Panel Master & Slave setup deals with the bypass, I haven't gone 
through to price it out to see if it makes sense yet, but I bet it does, 
especially since you can use dinrail breakers instead of all panel mount, as is 
the case with OutBack.

Not sure if you like or are planning on using the FlexNet DC, but on our 
install we had two inverters and two charge controllers, so the otherwise 
convenient triple-shunt-busbar option (OutBack) didn't really do much for us. 
Kinda dumb you can't use two FlexNet DCs... When I do it again I would probably 
steer the customer towards a Pentametric.

Ditto to the comments on the firmware upgrade and spacing the inverters. Next 
time I will definitely use a few nipples between the distribution boxes, the 
doors are way too tight when spaced right next to each other.

Cheers,
-Nathan

--
Nathan J. Stumpff
NABCEP Certified PV Installation Professional #091209-175
NABCEP Certified Solar Heating Installer #032412-14
Project Manager | Arctic Sun, LLC
[email protected] <mailto:[email protected]>  | (907) 457-1297
www.reina-llc.com<http://www.reina-llc.com/> | 
www.arcticsun-llc.com<http://www.arcticsun-llc.com/>
[cid:[email protected]]<http://www.facebook.com/ArcticSunLLC>

From: [email protected] 
[mailto:[email protected]] On Behalf Of William Miller
Sent: Monday, August 05, 2013 11:50 AM
To: RE-wrenches
Subject: [RE-wrenches] Dual Radian install

Friends:


I am bidding installation of two Radian inverters. Anyone out there done this 
yet?  Got any advice?

Thanks in advance,

William Miller


[cid:[email protected]]
17395 Oak Rd. Atascadero, CA 93422
www.millersolar.com<http://www.millersolar.com/>
805-438-5600 voice*
*Note: above number replaces cell number

<<inline: image001.png>>

<<inline: image003.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to