William,

I have a couple customers in a similar situation. The homes are Mexico and they 
need to operate mini split A/C for a few months. There is no space for 
increasing the PV array. Once the generator run time is balanced to maintain 
the batteries between 50% and 80% while also handling any heavy loads, the 
system can perform well daily. 

The downside is that this deficit charging will lead to early battery failure. 
The solution I use is to have a "Full Charge Day" bimonthly. The customer must 
operate the generator through the Bulk and Absorb charge and then start a 
short, high voltage equalization charge for about 2 hours followed by battery 
SG testing. This method is the best I could come up with and seems to be 
working well. During the other months, the PV system can keep up with 
consumption.

I too am getting more large system requests. If space is not a problem, I 
install large PV arrays to minimize generator use.

Larry



On Aug 16, 2013, at 12:53 PM, William Miller <[email protected]> wrote:

Friends:
 
We have been receiving a flurry of requests for design of off-grid systems 
where the loads are enormous, relative to normal off-grid requirements.  It is 
obvious that the size of PV and battery arrays to power these loads is beyond 
what is practical.  We have dubbed these systems Generator/battery with PV 
assist, or PV assist for short.
 
These systems will cycle batteries multiple times per day.  It is my 
understanding that the extra battery cycels will shorten battery life.  Since 
generator run is expected, we are willing to increase generator run time in 
order to prolong battery life.
 
The parameters I suggest are an aggressive load start and a very high battery 
start parameter.  This will prevent deep discharge of the battery bank.  I know 
shallow discharge is not the norm, but I don't believe shallow cycling is a 
problem as long is it as at the top of the voltage window, i.e. the batteries 
achieve absorption at least once per day.
 
We know a load start ciuld result in an abbreviated run time, curtailing 
absorption period, but we are assuming there will be a battery votage start at 
least once per day allowing full absorption.
 
Has anyone else considered these issues, and what conclusions did you make
 
I am looking forward to a spirited discussion as usual.  I throuroughlyenjoy 
and beneift from them, even thought the advice is usually conflilcting.  Thanks 
in advance.
 
William Miller
 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to