Carl, there are actually 2 (two) Sunny Island AC load output breakers.
One set is in the AC input-output bypass switch and the other are
separate breakers so you can turn off the inverter output.

The Sunny Boy outputs also go through a 2-pole circuit breaker.

What OCPD are you referring to ?

boB



On 9/16/2013 12:31 PM, Carl Adams wrote:
Hello Wrenches,

We are installing our first Midnite Solar E-panel for SMA. The epanel has a bus bar for landing the inverter output circuits. The attached diagram from Midnite does not include any OCPD in the circuit, but it seems to me these will be required . We'll be installing an SMA SB3000TL and SB5000TL. Have any of you installed this SMA E-Panel configuration before and if so how did you handle this piece of it?