Hi Marco;

Article 200.7 specifically prohibits using white wire for anything but grounded conductors. This came up last year on a large project with an ungrounded array, that also had white incorrectly specified in the plans. The appropriate colors would be red for positive, and black for negative.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 9/23/2013 1:27 PM, Marco Mangelsdorf wrote:

Hi all,

We're doing more and more installs with TL inverters (SMA and P1).

I'm using double-insulated wire from the array string to the first enclosure, as in j-box, and then transitioning to standard THHN/THWN wire.

I recently purchased some of that #10 double-insulated wire, getting a spool of black and white.

Then after receiving the two spools it occurred to me: since the array is ungrounded, as far as there being no grounded conductor in the circuit, did I blow it by getting a spool of white wire?

What sayeth you all? Can I not use that white wire in those array circuits for TL inverters?

Thanks,

marco



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to