You are right. Normally I would not even consider a generator of this size. My 
constant thinking outside the box took me down this rabbit trail. I'm back.

Thank you,

Larry 




On Oct 1, 2013, at 8:24 AM, Allan Sindelar <[email protected]> 
wrote:

Agreed. We're all offering ways to work as well as possible with the wrong 
generator choice for this application. 
Allan

Allan Sindelar
[email protected]
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
On 10/1/2013 9:16 AM, Ray Walters wrote:
> Sounds like they need a 20 Kw Kohler. Hot Tub in the future?  They'll love 
> their Kohler.  The Generac is just way too small to even consider IMHO. 
> 
> R.Ray Walters 
> CTO, Solarray, Inc 
> Nabcep Certified PV Installer, 
> Licensed Master Electrician 
> Solar Design Engineer 
> 303 505-8760 
> 
> On 10/1/2013 8:11 AM, Larry Crutcher, Starlight Solar Power Systems wrote: 
>> William, Chris, Ray, Allan, et al. 
>> 
>> Gen support would be ideal but this inverter setup will be a quad pack of 
>> Magnum 4024PAE (120/240 split; 16kW). Their New MSH inverter is single phase 
>> only and can not be stacked. 
>> 
>> While disabling load(s) is the antithesis of the desired outcome, I'll 
>> review this possibility further. 
>> 
>> Using a separate charger could work but it would need to be about 200A @ 32V 
>> which would add quite a bit of cost and be hard to sell since the Magnum 
>> inverters already have 4 high quality charges included. 
>> 
>> A larger generator might be necessary if the customer won't agree to load 
>> shedding. Their plans are to expand the loads over time, operate a business, 
>> install a hot tube and more. Of course I have pushed the concept that 
>> conservation is paramount. The PV array and inverters are being oversized 
>> now for the future growth. 
>> 
>> My ideal solution...Since Magnum inverters monitor the AC input and control 
>> it based on quality of power, it seems to me that there could be a setting 
>> for disconnecting the AC input if loads exceed a setpoint. Change in control 
>> software would be great. 
>> Thank you, 
>> Larry 
_______________________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to