A quick solution is to use a 2 to 3 prong adaptor and plug it into the GFCI, so that the equipment grounding function is isolated between the generator and the system wiring.

Ground the generator separately to a rod if it is fixed in place. If it is a portable generator, this isn't required, as the outlets on the generator still have the neutrals and equipment grounds bonded to the frame.

This method avoids parallel neutral currents, which are explicitly forbidden by the code.

At 09:57 AM 10/13/2013, you wrote:
Wrenches
I recently visited a site where their backup gen has GFCI outlets used for input to the FX inverter.
They finally tried to charge the batteries, and it trips the GFCI.
As a test I replaced it with a standard outlet and it works fine.
I have never used a gen with GFCIs, In fact most are hard wired.
Is the outlet the problem or is there really a ground fault?
Is there a safety issue?
I'm pretty sure the neutral and ground are bonded at the mains panel.

Thanks
Jeremy Rodriguez
All Solar

Sent by Jeremy's iPhone. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to