For 240 high-leg delta systems we typically use multiples of 3 SunnyBoys, which 
do not require a neutral connection.  Without the neutral the high leg is not 
an issue.  For smaller systems a single SunnyBoy also works well connected to 
phases A and C.  While the utility company may not be a fan of this, in some 
cases it can actually restore imbalance since many buildings with 240 delta 
have few if any loads on the high leg.

 

Contrary to their manual, Power-One also claims their smaller PVI inverters are 
compatible with 240 high-leg delta.

 

Garrison

 

Garrison Riegel

Project Manager |  <http://www.solarserviceinc.com/> Solar Service Inc

[p] 847-677-0950 |  <mailto:[email protected]> 
[email protected]

 

NABCEP Certified PV Installation Professionalâ„¢

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, October 17, 2013 10:49 PM
To: [email protected]
Subject: Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

 

Chris Mason wrote:

 

>SMA just came out with their Sunny Tripower line for the US. 

 

Yes those are interesting. But they are only for 480 Wye, not 240 Delta.....

Is the Fronius 11.4-3 the only 3-phase inverter that can work with 240 3-phase 
with a hi-leg (stinger)?

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to