Howie,

I've looked at a few different MC cable manufacturer data sheets and I can't 
find a distinction between AC or DC. In general I wouldn't expect there to be a 
difference since AC RMS voltage and current ratings are sort of a 'DC 
equivalent'. But the only way to be sure is contact a cable manufacturer and 
ask a specialist. There could be something buried in the listing. And we all 
know it is expensive to get a hold of UL standards to look the damn thing up 
ourselves.

Example MC cable data sheet:  http://www.afcweb.com/pdf_2011/p12_mc_s_lt.pdf

I am guessing that John Wiles was referring to 690.31(E) which has to do with 
running inside a building with DC conductors before hitting a DC disconnect. 
This section was changed in 2011 NEC to include MC cables specifically. Maybe 
from this it got lost in translation back to you?

Good luck,

Jason M. Szrom, PE
Engineering Supervisor
Solar Energy Systems, LLC
718-389-1545 x13

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Howie Michaelson
Sent: Monday, October 21, 2013 2:15 PM
To: RE-wrenches
Subject: [RE-wrenches] MC Cable for DC runs

Hi All,

Just had a conversation with an electrician friend who took a John Wiles course 
for inspectors a couple of weeks ago, and he thought (but wasn't
sure) that John said in order for it to be code to use MC cable for PV homeruns 
inside the building envelope, the cable needed to be rated for DC.  This was 
new information to me, particularly since I've never heard of MC cable being 
rated specifically for DC.  Is this accurate information, and does anyone know 
what the wire spec would be for this?

Thanks,
Howie
--
Howie Michaelson
NABCEP Certified Solar PV Installer(tm)

Catamount Solar, LLC
Renewable Energy Systems Sales and Service VT Solar Electric & Hot Water 
Incentive Partner http://www.CatamountSolar.com
802-272-0004





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to