Hi Jeffe, I don't know the specs on those Kyocera, but if they are the same VOC then they are fine together.
As to a enclosure for the CC's, I'd look at Midnight. They have about a million different boxes, you'll find one that will do the job for you I'm sure. Depending on the area, you might look at a midnight 150v, or 200v or 250v controller, as you can then run all in series. jay peltz power On Oct 24, 2013, at 1:13 PM, Jesse Dahl wrote: > Hello, > > Looked at a system today that consisted of the following: > > 15 - Kyocera 158W modules > 3 - Kyocera 185W modules > 1 - Outback MX60 > 8 - New Trojan L16RE (48V system) > 1 - Xantrex SW Plus > > 6 months ago he swapped out his old charge controller to the new MX60 and > purchased the new batteries at that time. The array wiring did not change > and is wired in 6 strings of 3. (confusing to the MX60?) > > He is now adding 4 Kyocera 240W modules. He also purchased another MX60 for > this array. > > From my perspective, removing the 3 185W modules and getting them on their > own controller would be a better use of the modules. The system currently > does not have any disconnects on the PV side. There are fuses in the > combiner boxes on the array, but no disconnects inside at the charge > controller. So adding 3 charge controllers, and now needing to add GFDI, > means a box of some kind needs to be added to house these breakers. > > Outbacks GFPs and panel mount breakers will work, but what is the best > mounting solution for these? One DC Flexware enclosure? It will of course > allow for all the DC OCPD and allow for the landing of the output of the > charge controllers. Or is there another enclosure/OCPD solution I should > look at? > > > Thanks as always! > > Jesse > > > > > _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org