W:

A string inverter does not constitute a separately derived system unless it is 
transformer isolated. The recreating of the neutral is what creates an SDS. 

Your GEC, if required, stops at the inverter. It is not always required, i.e. 
Enphase M250. 

William Miller

> On Nov 9, 2013, at 1:53 PM, "Wallace W. Weeks" <[email protected]> wrote:
> 
> Wrenches,
> 
> On a recent install I've come across a question I would like to get your 
> thoughts on. 
> 
> In regards to running a GEC on a "separately derived power system",  more 
> specifically A single phase 600 v residential PV system with a string 
> inverter.
> 
> From my past experience and building from approved plansets throughout the 
> bay area and Monterey Counties. I have always pulled a #10 ground with my DC 
> conductors.
> 
> A recent conversation sparked The idea a local jurisdiction wanted a GEC 
> (minimum # 8 AWG In conduit & #6 bare free air) pulled from the roof to the 
> inverter ? Also #6 bare bonding the rails ?
> 
> Furthermore The GEC coming from the array shall not be permitted in FMC? The 
> scenario was transitioning from EMT to FMC in an attic.
> 
> Referencing and potentially misinterpreting 
> 250.64 B,  It does seem to exclude FMC from approved means of protection ?
> 
> My questions are as follows.
> 
> -Is it a common requirement to bond rails with # six bare & run a GEC from 
> the roof to the inverter ?
> 
> -Why would the transition from EMT to FMC not be acceptable because the GEC 
> is in the raceway ? when In a scenario that is free from damage. For example 
> in attic ?
> 
> Thank you for your clarification on these topics.
> 
> Cheers-W.W.W
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> Sent from W.W.W'S iPhone
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to