Wrenches,

There is no guidance in the Code text for where the shutdown should take place. 
(1) says: "Requirements for controlled conductors shall apply only to PV system 
conductors of more than 1.5m (5') in length inside a building, or more than 3m 
(10') from a PV array."

So, the provisions apply if the circuit 10' from the array and 5' inside a 
building, but no mention is made of where the shutdown actually needs take 
place in the circuit. In the video Bill Brooks suggests that the shutdown 
mechanism should also be placed within this 10'/5' boundary but that is just an 
inference -- nowhere in the text is this actually specified. If that was the 
intent of the Code committee, then they've done a poor job actually expressing 
it in English.

I'm concerned that some AHJs will interpret this to exclude all central 
inverter systems (without the addition of cost-inducing secondary DC-DC 
converters like Tigo) because the combiner or junction box can be many feet 
from the actual beginning of a home run under the array. Alternately, 
permissive AHJs could allow this function to be fulfilled anywhere, meaning 
that the implementation won't meet the intent of the writers.

I'm also concerned, as Isaac mentioned, that there are no requirements for how 
the shutdown be initiated, or that it contains of the accessibility and 
grouping requirements that are always included for disconnects. I really think 
this should be treated and categorized as a disconnect requirement, not a 
circuit requirement, because that is the ultimate function that's intended. 

I'm surprised none of the inverter manufacturers have chosen to comment here, 
as this could dramatically impact the sales of central inverters.


Jeffrey Quackenbush
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to