The project is hybrid, the house has utility power at the moment.
I was looking for feedback on the product, I haven't heard comments on the
Outback RE battery system.
In the end I recommended a single string of TROJAN, IND9-6V. We will revert
to grid at 80% DOD.
The house is tropical, high in the mountains and doesn't use a lot of power.





On Sun, Jan 19, 2014 at 9:22 PM, Allan Sindelar <
[email protected]> wrote:

>  Tom,
> I may be mistaken, but if I understood you correctly you have missed
> something. The Radian is available only in 48v, so four 12V 200 Ah
> batteries is eight kilowatt-hours of storage to 80% maximum DoD. Yes, it's
> small (my off grid home has 26 kW) but one or two strings may be adequate,
> depending on the customer's application and needs.
> Allan
>
>       *Allan Sindelar*
> *[email protected]* <[email protected]>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder, *Positive Energy, Inc.*
>
> A Certified B CorporationTM
> 3209 Richards Lane
> Santa Fe, New Mexico 87507
> *505 424-1112 <505%20424-1112> office 780-2738 cell*
> *www.positiveenergysolar.com* <http://www.positiveenergysolar.com/>
>
>
>   On 1/19/2014 6:12 PM, Tom Duffy wrote:
>
>  Hi Chris
>
>
>
> For an off grid system a 200AH 12 volt battery is rather small without
> resorting to parallel strings.
>
>
>
> Three strings is only 600AH which is still on the small side, so one might
> ask why the 8K inverter?
>
>
>
> The OutBack cabinet is fine for a back-up grid-tied system, not really a
> full off grid house
>
>
>
> Without starting a big discussion, I would stick to a single series string
> sized to the load for three days autonomy.
>
>
>
> 200AH is usually a rather small weekend cabin and 600AH would be a smaller
> medium sized house.
>
>
>
> Kind regards
>
>
>
> *Tom Duffy*
>
> *Senior Solar Design Engineer*
>
> [image: Real-logo-X-195]
>
> *E-Mail: **[email protected] <[email protected]>*
>
> *Panama Office: **507-6126-1253*
>
> *Direct Toll Free:**888-503-6772 <888-503-6772>*
>
> *International: **575-539-2111 <575-539-2111>*
>
> *SKYPE Address: **thesolarbiz*
>
> *Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced.*
>
>  *Confidentiality Notice*: This message including any attachments is for
> the sole use of the intended recipient and may contain confidential and
> privileged information. Any unauthorized review, use, disclosure or
> distribution is prohibited. If you are not the intended recipient, please
> contact the sender and delete any copies of this message.
>
>
>
>
>
> *From:* [email protected] [
> mailto:[email protected]<[email protected]>]
> *On Behalf Of *Chris Mason
> *Sent:* Saturday, January 18, 2014 6:16 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Outback 200 RE
>
>
>
> We don't do a lot of off-grid systems so I am short on experience with
> battery systems. I have a 8KW Radian system for which I am considering
> Rolls Surrette or Outback 200RE AGM batteries. I know people like the
> Surrettes, what is the experience with the outback battery system?
>
>
>
> --
> Chris Mason
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Change email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: [email protected]
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts

<<image/png>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to