I'm definitely interested in being involved too. I really respect how difficult the language crafting can be, and the frustration to have certain intent be misconstrued by an AHJ some where else later.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/23/2014 4:17 PM, Dan Fink wrote:
Thanks for the correction on that sedona fire Bill; I had only seen the incorrect fire dept report. I wish there was a clearinghouse for information on RE incidents and close calls as they are all teachable moments for both RE professionals and firefighters.

I ditto the need for more NEC guidance on battery banks. In my firefighting career, I've been at about a dozen structure fires involving RE equipment. Only 4 were actually caused by the RE equipment. *All* of those originated in or near the battery bank. 1 internal battery short circuit, 1 mouse chew inside battery box, and 2 bad connection when charging with a generator.

I'd like to get involved, Bill....I have lots to say about wooden battery boxes, parallel fusing, signage, and more. What are the first steps for getting involved?


Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342



On Thu, Jan 23, 2014 at 12:23 PM, Bill Brooks <[email protected] <mailto:[email protected]>> wrote:

    Jeffrey and Ray,

    Batteries can off-gas hydrogen-sulfide gas when under heavy charge
    or overcharge. It is the nasty rotten egg smelling gas. Definitely
    not to be inhaled since when it hits your lungs it turns back into
    sulfuric acid.

    To address Ray's point, the new 690.12 regulation that has been
    getting a lot of air time on this list does, in fact, address
    battery circuits for PV systems. Any circuit that is part of a PV
    system inside a building within 5' must be controlled to 30V,
    240VA within 10 seconds. This includes all the ac output
    conductors from a backup PV inverter and the battery inverter
    input circuit as well. This provision matches the new requirement
    for battery systems in 690.71(H) that requires "A disconnecting
    means and overcurrent protection shall be provided at the energy
    storage device end of the circuit. Fused disconnecting means or
    circuit breakers shall be permitted to be used." Ideally we try to
    keep our battery conductors to 5' or less and that means that no
    additional disconnecting means would be necessary according to the
    new 690.71(H). If we have to go longer than 5' and the conductors
    are inside the building, a rapid shutdown capability would need to
    be on that circuit and it would need to have a disconnecting means
    and overcurrent protection. The best way to meet this requirement
    would probably be to have a shunt-trip breaker, similar to what
    Midnite Solar provides with their birdhouse setup.

    There are definitely much more discussion going on in the NEC
    about energy storage now than ever before. This next code cycle
    will be very busy on the subject. It is likely that article 480
    will soon be turned into "Energy Storage" or a new article in
    Chapter 6 or 7 will cover "Energy Storage Systems." It was
    proposed last cycle and failed, but this time there is much more
    interest in the subject. The solar industry needs to be involved,
    so it sounds like this is your year for both of you to get involved.

    Bill.




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to