William,

Are those the older Sunny Island 4.2 or 5kW units, or the newer 4.5 or 6kW 
units?

Is this single-phase or three phase?

The SMA BATFUSE would work, but it is not available in the US. It's not Code 
compliant nor UL Listed.

You could use the OutBack FW1000-DC, but you are going to have a little fun 
doing the DC cabling and conduit. The older Islands had dual 1/0 battery 
terminals. The newer ones have a single 3/0 terminal. Unfortunately, those 
sizes are hard to find in proper flexible battery/inverter cable, mostly 
because it doesn't sell in enough volume for distributors to carry. It also 
doesn't properly match available DC breaker sizes, like 4/0 and 2/0 cable does.

SMA worked directly with MidNite Solar to develop the MidNite E-Panel system 
for the Sunny Islands. It's what I would recommend using. For one thing, they 
have dealt with the DC cable and fusing size issues (and, no, you are not 
blind). You can run 2/0 (4.2 or 4.5kW units), or 4/0 (5 and 6kW units) to the 
E-Panels

However, I don't know offhand if they work with the older Islands. If you are 
dealing with the older units, you should contact them to confirm that they will 
fit.

If it's three-phase at 208 VAC, I also recommend that you use one of the 
MidNite three-phase Master units (MNE250SMA-3PH-Master) and two slaves. It has 
a three-phase bypass switch and color-coded bus bars for a full three-phase 
system. There isn't a whole lot in there that you won't likely use. The AC 
output on the bypass will just act as an AC main breaker. You can then run that 
to an external load center.

Now, the distance from the battery bank issue is new. These systems have been 
installed for a couple of decades now with up to 12 feet between the battery 
and the first disconnect, breaker, or fuse. Of course, that doesn't make it 
right, or compliant with the 2014 Code. The industry really needs to come up 
with a good solution here. The Wrenches thread over the last few days about 
placing fuses on or near batteries shows that an easy solution is not available 
(or not known), at least not for flooded batteries.

Brian Teitelbaum
AEE Solar

From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, February 07, 2014 5:29 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Sunny Island Battery Disconnects

Friends:

I am reworking an installation with 3 Sunny Island inverters.  The battery 
leads have no disconnecting means or OCP.  I have been looking for sensible 
hardware to provide this and I have found some options.  I am interested in any 
input on these or ideas I have not discovered.


1.       SMA BATFUSE.  I am having trouble deciding which one is right for a 3 
SI install.

a.       The B.003 appears to have fuse positions for the positive and the 
negative leads.  I am fairly darn certain I don't want fuses in the negative 
leads of a negative bonded system, and although this is my first SI install, I 
am pretty sure this is negative bonded.  Am I missing something here?

b.      The B.001 has only positions for two fuses as far as I can see from the 
manual.

c.       So it looks like neither will work for me.  Does anyone have any 
experience and/or wisdom here?

2.       Midnite Solar E-panels:

a.       The regular panel has DC and AC components.  I want to control the AC 
elsewhere so I could order three slave units.  The Midnite unit mounts right 
under the inverter but I would prefer to have the OCP closer to the batteries.

3.       Outback:

a.       We could purchase an Outback FX1000 and install three breakers in it.

4.       Breaker Size:

a.       I have started to read the manual but I have yet to find out what size 
breaker fuse is recommended.  Have I just not found it yet?

b.      Also, I have not found a specification for battery cable size.  Am I 
blind?

Thanks in advance.  I really appreciate the help I receive here.  I try to give 
as well as receive.

William


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to