Jay:
It is meant for installation immediately adjacent to the inverters. I believe we need to be installing OCP adjacent to the batteries. Wm From: [email protected] [mailto:[email protected]] On Behalf Of jay peltz Sent: Tuesday, February 11, 2014 6:56 AM To: RE-wrenches Subject: Re: [RE-wrenches] Sunny Island battery OCP HI William, I agree with your choices below, but I"m curious why you decided against the midnite Epanel for the SI? thanks jay peltz power On Feb 10, 2014, at 9:33 PM, <[email protected]> wrote: Friends: Thanks for all of the replies. Here is what I have learned so far 1. The SMA fuse blocks are not UL listed for installation in the USofA. 2. The Square D switches are not high enough in amperage for battery circuits. 3. The bolt-switch idea is great if you want fuses and a pullout. Not for me. 4. Our solution will be an Outback FX 1000 with three 250 amp breakers.
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org