I wholeheartedly concur with the critics here. [rant mode on]

I've long been very critical of certain elements of the Electric code...But the 
state fire Marshall guidelines are approaching outrageous. 

I feel very let down by the industry advocates, trade groups, and especially 
those directly involved in the rule making process... They're supposed to have 
the public's interest foremost in mind---code standards are supposed to be 
based on the rigorous test that they demonstrably prevent loss of life and loss 
of property at an economically justified cost. Instead, it seems, the 
rule-making has advanced to secure a role for continuing stream of proprietary 
and incrementally more costly "safety" hardware along with a secure role for 
those in the process to secure themselves a reliable permanent stream of 
consulting gigs training and retraining ever more complex and unintelligible 
code rules.


/wk

William Korthof
714.875.3576
Sustainable Solutions
#956904

On Feb 14, 2014, at 2:27 PM, Dan Fink <[email protected]> wrote:

Hi Bill;
That was tongue in cheek about watching my back! But wow I've seen the 
discussion get heated, even in face to face outreach sessions. The firefighter 
you refer to is one of the top teachers on the topic in the US. Providing an 
escape route on the PV side of the structure is really critical. And I think 
it's fair to say that the larger the percentage of the roof that can't be 
ventilated, the more difficult and dangerous it is to save the structure, and 
the less likely the FD will try. 

And -- interior sprinklers! What a concept, not rocket science, and knocks out 
about 95% of this whole discussion. Mandated in new subdivisions in my area.

Labeling! SHUT DOWN SOLAR HERE in big red letters outdoors, etc.

I'll keep trying to do my best as a go-between betwixt the fire service and RE, 
one PV installer and one fire department at a time.

Best regards; 

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342

 


On Fri, Feb 14, 2014 at 12:23 PM, Bill Hennessy <[email protected]> wrote:
> hi dan--you weren't the firefighter--it was some guy from california given a 
> guest column. no reason to watch your back.
> 
> my point is that there is no real data about fire problems from pv and we're 
> talking two different worlds between a huge cold storage facility in an urban 
> setting and residential rooftop a long ways from the fire station. i don't 
> see the need to rule make for situations that might happen, effectively 
> throwing out the baby with the bathwater. 
> 
> if pv is to blame in some instance for an increased loss of property, so be 
> it. but what about the truck that runs into somebody's living room. do we 
> install bollards in front of the rest of the houses on the street? 
> 
> regards, bill
>  
> Bill Hennessy
> Berks Solar, LLC
> 371 Centennial Rd
> Mertztown, PA 19539
> 
> o 610 682 4300
> c 484 560 4666
> NABCEP certified installer
> PA contractor #44411
> www.berkssolar.com
> 
> From: Dan Fink <[email protected]>
> To: Bill Hennessy <[email protected]>; RE-wrenches 
> <[email protected]> 
> Sent: Friday, February 14, 2014 1:22 PM
> 
> Subject: Re: [RE-wrenches] California State Fire Marshal's "Solar 
> Photovoltaic Installation Guidelines"
> 
> Bill H;
> I believe I'm the firefighter you are referring to, and I'm allowed here on 
> the Wrenches list because I've been a professional RE installer since 
> 1994--still my career-- and a firefighter in a rural area  with a large 
> percentage of PV and wind installs. A couple talking points:
> 
> ~Thanks Bill Brooks for explaining here why the roofing class ABC rating 
> system has nothing to do with firefighter rooftop access/egress.
> 
> ~Unfortunately ventilating the other side of the roof doesn't always work, 
> wind from the wrong direction, wrong internal compartment in the structure, 
> etc. Also we use chainsaws with carbide teeth, the axes are for flipping open 
> the roof sections; And egress is a problem...do we hang roof ladders from PV 
> modules to escape a roof collapse to the other side?
> 
> ~A fire commander will *never* risk the lives of his responders to the 
> unknown. Instead the answer will be indirect attack - protect exposures - let 
> it burn. As a RE professional it is *your*  job to provide safe designs and 
> installations, label everything simply, obviously and properly as to what is 
> there and how to shut it off, and more importantly reach out to your local 
> fire department with the details on the systems you have installed in their 
> response area, so if they get a call there, they know exactly what they are 
> dealing with in advance. The more they know, the higher the chance they can 
> save the house.
> 
> ~ There has been at least one high-profile and high-dollar "let it burn" case 
> in the last year. Not good for the PV industry.
> 
> Will see many of you in Denver next month. Somehow I feel like I better keep 
> watching my back.....yikes.
> 
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckville Publications LLC
> NABCEP / IREC accredited Continuing Education Providers
> 970.672.4342
> 
>  
> 
> 
> On Fri, Feb 14, 2014 at 9:20 AM, Bill Hennessy <[email protected]> wrote:
> Andrew--Thank-you for your work to dampen the fire hysteria that's sweeping 
> the roofs of residential solar. Between the ridiculous setbacks (out here 
> you'd never see a firefighter on a house roof swinging an axe, but if so 
> inclined, they could go on the other side of the peak).
> 
> And now we need to install mythical products for de-energizing and 
> fire-protection racking. Unless the big leasing companies can beat back the 
> anti-solar "safety" club, rooftop residential is toast. PV leaders and 
> consultants have caved. A short time ago, a firefighter (what was he doing on 
> the wrench page anyways?) urged installers not to look at their bottom line 
> and take in the big picture.
> 
> That is exactly what you are doing in opposing these rules that are set up 
> for problems that don't exist. The firefighting and code making industries 
> are big bucks. 
> 
> Let's see, wrenches and folks who write the code can't figure out what it 
> says. And in our county in PA, there are 90 different permitting agencies 
> that will be reading the same codes and ordering their interpretations before 
> we get a permit.
> 
> The real big issue is sustainability and climate change and we need to have a 
> society that embraces a rush to PV and not smother it with the love of 
> safety. Want to stop fires? Let's go after toaster ovens.
>  
> Bill Hennessy
> Berks Solar, LLC
> 
> 
> From: Solar Energy Solutions <[email protected]>
> To: RE-wrenches <[email protected]> 
> Sent: Thursday, February 13, 2014 3:13 PM
> Subject: Re: [RE-wrenches] California State Fire Marshal's "Solar 
> Photovoltaic Installation Guidelines"
> 
>  
> Today at 11:41 AM
> Dear colleagues,
> 
> Rooftop real estate available for solar is of unparalleled and monumental 
> importance.  As we head into our 6th great extinction the solar industry 
> needs to fight tooth and nail to gain 100% access to every inch of available 
> roof space.  The fire fighting industry needs to adapt to solar, NOT vice 
> versa. 
> 
> In Oregon, one person, myself, stopped the 12 person BCD committee from 
> adopting the anti solar 3 foot pathway around solar arrays.  The committee 
> would not listen to reason.  I went to the governors office saying and 
> showing that if the Cal. Guidelines were adopted as code 100% of the roofs we 
> had installed systems on would be 100%illegal and unviable.
> 
> Yada yada yada, we got the Koyaanisqatsi Rule.
>  
> 304.9.1 General Pathway Requirements
> Exception
> 1.1. Where the PV array does not exceed 25% as measured in plan view of total 
> roof area of the structure, a minimum 12 inch (305mm) unobstructed pathway, 
> shall be maintained along each side of any horizontal ridge.
> 1.2. Where the solar array area exceeds 25% as measured in plan view of total 
> roof area of the structure, a minimum of one 36 inch (914 mm) unobstructed 
> pathway from ridge to eave, over a structurally supported area, must be 
> provided in addition to a minimum 12 inch (305 mm) unobstructed pathway along 
> each side of any horizontal ridge.
> 
> I still see this as a failure.  I had 40% going into the final meeting and 
> one foot from the peak only on pitches greater than 4:12.  But, by that time 
> everyone hated me soooo badly for holding such a hard lined solar centric 
> perspective, and for succeeding in going over their heads, it was all I could 
> do to get them to meet.
> 
> Unassisted in this battle I was exhausted and unable to follow the 
> proceedings to the end.  And, in the end, a rafter span chart hostile to 
> solar was thrown in and now we are dealing with that.
> 
> Here is the link to the  Oregon Solar Installation Specialty Code:  
> http://www.cbs.state.or.us/bcd/programs/solar/solar_code/100110_OSISC.pdf
>  
> The concept and good intentions of a statewide code were good.  
> Unfortunately, the task was left to folk who were not as friendly towards or 
> knowledgeable of solar as one would think would be asked to be part of such a 
> noble cause. 
> 
> Respectfully Submitted,
> 
> 
> 
> Andrew Koyaanisqatsi
> President
> Solar Energy Solutions, Inc.
> Since 1987,
> Moving Portland and Beyond
> to an Environmentally Sustainable Future.
> 503-238-4502
> www.SolarEnergyOregon.com
> "Better one's House too little one day
> than too big all the Year after."
> 
> 
> On Thursday, February 13, 2014 11:45 AM, Mark Frye <[email protected]> 
> wrote:
> There are so so many well informed people on this list, and I am so lazy.
> 
> I wish someone could just lay it all out":
> 
> We got the 2012 ABC thing nearly identical to NPPA1 with the set backs 
> and labeling
> We got the 2014 NEC with the de-energizing the conductors and equipment
> We got the IBC which appears to say one thing about fire rating ie. 
> needs to be the same as roof
> And we got the UL thing that seems to be based on the combined rating of 
> the module and racking system
> 
> Wow, I commend anyone who is willing to go into a building department 
> and lay down a set of plans.
> 
> Mark
> 
> 
> On 2/13/2014 10:50 AM, William Korthof wrote:
> > Bill,
> >
> > Thanks for the attached info. I don't see where the fire rating class of 
> > solar modules is addressed though...
> >
> > In the IBC, the specific section (I believe 902.4 or close to that) seems 
> > to call for solar modules to carry the same fire rating class as the 
> > roofing class required of the building. At least that's the interpretation 
> > I initially got from my local building and safety office. They've been 
> > sitting on my plans for two weeks so far. When they turn them around, I may 
> > have more to talk about.
> >
> >
> > /wk
> >
> > William Korthof
> > 714.875.3576
> > Sustainable Solutions
> > #956904
> >
> > On Feb 13, 2014, at 9:34 AM, "Bill Brooks" <[email protected]> wrote:
> >
> > Yes Peter,
> >
> > It is called the 2012 International Fire Code. The California guidelines
> > were turned into code in 2012. There is an explanation document I wrote
> > available online at:
> >
> > http://solarabcs.org//about/publications/reports/fireguideline/index.html
> >
> > For those states that are using NFPA 1 as their fire code, it is nearly
> > identical.
> >
> > Bill.
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: [email protected]
> >
> > Change email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: 
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> 
> >
> >
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to