Thanks for the feedback.  Turned out to be 3 separate issues.  The AC backfeed 
turned out to be mostly caused by a missing neutral to ground bond.   With that 
corrected, the backfeed dropped from 30 volts to 2 volts on one leg only... 
still a puzzle.  Other issues were a snow and ice covered regulator which may 
or may not have affected the starting.,  Also the magnetic pickup for frequency 
control was weak and the Kohler guy replaced it.  At one point today the 
generator was just a pile of rubble in the snowbank... wish I had taken a 
picture.  He got it all back together and it ran fine, we reconnected to the 
radian with the 2 volt backfeed and it worked fine.  Time will tell if we still 
have a problem. 



-----Original Message-----
From: Jerry Shafer <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Mon, Feb 17, 2014 3:49 pm
Subject: Re: [RE-wrenches] AC Backfeed from Radian.


If you disconnect the leads to the Benny from at the inverter do you still have 
this condition. I had a battery charged supply (ac) in the same conduit as the 
remote start and the transient voltage would be enough to signal z start up. 
Your issue is a little different but it might still be transient
Jerry
On Feb 16, 2014 7:02 PM, "john" <[email protected]> wrote:

Wrenches,
    I have an off-grid installation with an Outback Radian using a Kohler RES 
13 for backup.  The generator has had problems from day one and has had control 
boards replaced and other work done on it.  This system started out with a 
Magnum 4024AE but was undersized for the loads and battery size so we upgraded 
to the Radian.  The current problem is the generator running erratically 
(frequency and voltage) and running rough.  The Kohler repairman said that the 
problem is that the inverter had damaged the generator with a measured 12 VAC 
at the inverter side of the AC IN breaker when the generator is off.  When I 
arrived, we started the generator with the MATE 3 and it worked fine for about 
10 minutes charging at 4.5 kw and then the engine started running erratically.  
The frequency readout on the MATE 3 ranged from 56 Hz to 67 Hz and the voltage 
was sometimes steady at 238 and at times varying from 236 to 244.  The MATE 3 
showed several manual starts previously where the Initial voltage was 277 
briefly (1 second) and then leveled out and locked on. Eventually the generator 
shut down with Error 13.  We also had it fail to start with Locked Rotor error. 
 I did measure 3.1 VAC on the AC out bus of the inverter when the generator was 
stopped.  Is that small voltage present normal for the Radian and is there any 
way that could affect the generator?   When I set the MATE 3 to DROP to 
disconnect the charging, we could still read the hz and Voltage at the bus and 
the erratic behavior continued.  I think there are serious problems with the 
generator but the Kohler tech says it is the inverter interference .  When we 
started the generator manually with the input breaker off, it ran erratic and 
eventually shut down.  


The customer wants the generator guy and myself there tomorrow to figure out 
how to fix it.   I say a new generator might take care of the problem but the 
customer doesn't want to hear this.
Any ideas?  I have dealt with lots of generators and to me this seems like a 
worn out genny. 


John Blittersdorf
Central Vermont Solar & Wind  






  



 


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to