If the subpanel is at the end if the feeder, and there are no taps in between 
the main and the sub then I don't see any reason that the conductors need to be 
any larger than 200 A as there is no where on the feeder conductors where grid 
and PV current will be additive. 

The changes in 705.12 in 2014 address this in large part. 

Brian

> On Mar 4, 2014, at 2:41 PM, "Kirk Herander" <[email protected]> wrote:
> 
> Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The 
> feed-in subpanel is also powering unrelated loads, which use the neutral as a 
> conductor from the main panel. So 4 conductors from the main.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Allen Frishman
> Sent: Tuesday, March 04, 2014 4:32 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> what inverter(s) are you using?    In many cases the Neutral is not 
> considered a Current Carying Conductor by the Manufacturer and therefore you 
> only have 3 CCC.
> Al Frishman
> AeonSolar
> (917) 699-6641 - cell
> (888) 460-2867
> www.aeonsolar.com
>  
> On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:
> 
> 
> Approx.. 50 – 60ft.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ray Walters
> Sent: Tuesday, March 04, 2014 4:05 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> What is the length of the conduit to the subpanel? That will determine 
> whether to apply the derates.
> 
> 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 3/4/2014 1:34 PM, Kirk Herander wrote:
> Whether or not a further derate has to be applied is the killer here, as I am 
> working with existing panels and conductors. In an old Code Corner(HP140) J. 
> Wiles goes through a similar scenario and calls out the allowable current 
> rating and conductor in 310.15, but makes no mention of applying additional 
> derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the 
> existing 4/0 cable between feed-in and main panel at 208 amps, less than the 
> allowable 217. I’d hate to need to upsize the wire to 250 mcm.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Jason 
> Szumlanski
> Sent: Tuesday, March 04, 2014 2:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> Both the bus and conductors need to be rated for 217 amps minimum. As you 
> mentioned, the bus is not a problem. The way I interpret it, the conductor 
> size required would be after derate factors are applied. The rating of the 
> conductor is ultimately dependent on the derate factors.
>  
> If you can locate your subpanel adjacent to the main distribution panel, you 
> may be able to use Exception #3 to 310.15(B)(2) by connecting the panels with 
> a short nipple. I assume you are just looking at a number of conductor derate 
> and not an ambient temperature derate.
>  
> Jason Szumlanski
> Fafco Solar
> 
>  
> <image001.jpg>
>  
> 
> On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander <[email protected]> wrote:
> Hello,
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker. 
> My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 = 
> 270 amps. That’s less than the sum of the two breakers of 260 amps, so no 
> issue there. The conductors between sub and main panel have to be rated for 
> at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after 
> derating the conductor?
>  
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
>  
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
>  
> List Address: [email protected]
>  
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>  
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>  
> Check out participant bios:
> www.members.re-wrenches.org
>  
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to