Ah...OK

Looks like you have two options:

Locate the shop's inverter on the house, and run 240 VAC the 100 feet to the 
shop, where it will connect at the shop's service entrance.

Or, locate the inverter at the shop, and run the PV array DC the extra 100 foot 
distance.

Which is better? Electrically, I don't think that it really matters much.

With the inverter on the house, you are adding a 100' of AC wiring, so you need 
to make sure that any voltage drop does not cause the inverter to operate at 
too high an output voltage. If the utility service has already higher than 
normal AC voltage, that could cause the inverter to shut off due to high AC 
voltage. Running that distance as DC would not give you that potential issue. 
You still lose some power due to voltage drop of course (either AC or DC), but 
as long as that doesn't cause the inverter to operate below its MPPT DC voltage 
window, it won't effect it.

In either case, you will need an approved disconnect at each location, in other 
words, on each end of that 100' line. And good signage.

And I would recommend surge/lightning protection on both ends.

However, if you have the shop's inverter on the house, that also means that you 
have an AC connection from the shop's Service present at the house. This is 
where 230.2 may apply. You have two separate buildings with two separate 
Services. 230.2 applies to single, or physically connected, buildings with 
multiple Service entrances. It's about safety, so that fire fighters or other 
emergency personnel can be sure that if they pull a service meter, that they 
are cutting all the power to that structure. If you have an AC connection to 
that other Service, the AHJ may take issue with it under 230.2, even if you 
have a lockable disco,  good signage, and the house meter and shop disco are 
close together. You should consult with your AHJ.

Brian Teitelbaum
AEE Solar




From: [email protected] 
[mailto:[email protected]] On Behalf Of Nathan Charles
Sent: Friday, March 14, 2014 2:23 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Two systems on one building with separate services

No, the shop service is located on the shop building.

-N

On Fri, Mar 14, 2014 at 4:52 PM, Brian Teitelbaum 
<[email protected]<mailto:[email protected]>> wrote:
Are both services (and meters) on the house? Or is the shop service located on 
the shop building?

Brian

From: 
[email protected]<mailto:[email protected]>
 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Nathan Charles
Sent: Friday, March 14, 2014 1:43 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Two systems on one building with separate services

The distance between the building is about 100'.

The residential service is a 200A service but the workshop is 400A because of 
large of equipment and can't be combined at this point.


On Fri, Mar 14, 2014 at 4:03 PM, Brian Teitelbaum 
<[email protected]<mailto:[email protected]>> wrote:
Nathan,

What is the distance between the buildings, and where are the utility meters 
located?

What are the sizes of the Services? 200A?

Can both buildings be powered from a single Service? Why is the workshop 
metered separately?

Brian Teitelbaum
AEE Solar

From: 
[email protected]<mailto:[email protected]>
 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Nathan Charles
Sent: Friday, March 14, 2014 12:05 PM
To: RE-wrenches
Subject: [RE-wrenches] Two systems on one building with separate services

Hi Wrenches,

I've got an issue that's got me stumped and I was hoping somebody could give me 
some suggestions.

We have a customer who has two meters, one on the house and one on a workshop.  
The workshop is heavily shaded and it's zoned residential so meter aggregation 
isn't a possibility.   The customer is hoping to put two separate PV systems on 
the house one for each meter with the inverters mounted in the garage.  It 
seems like that sets me afoul of the intentions of 230.2 Number of services, 
but if I remote one set of inverters and run DC I'm not quite sure how to think 
through the disconnecting requirements.

Any advice or suggestions on if or how this might be possible?

--
Nathan Charles
Engineer
NABCEP Certified PV Installation Professional #042013-20
Paradise Energy Solutions


_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



--
Nathan Charles
Engineer
NABCEP Certified PV Installation Professional #042013-20
Paradise Energy Solutions
(717) 283-2021<tel:%28717%29%20283-2021> direct

_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>




--
Nathan Charles
Engineer
NABCEP Certified PV Installation Professional #042013-20
Paradise Energy Solutions
(717) 283-2021 direct
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]