Dan,
It took me a bit of reading replies to understand the issue you
are addressing. If the issue is as simple as not running 240V
loads off of a panel supplied by 120V inverter output, then you
have three approaches. You would expect to run off of either a
pair of inverters set up for 120/240, an inverter with the same
capability (Magnum AE, Radian, XW or Conext SW, etc.), or a single
120V inverter (FX/VFX, SW4024, etc.) with a step-up
autotransformer. If the latter, consider running 120V only to the
main distribution breaker panel, and separately running the 240V
loads, either directly from the autotransformer output (a single
load, such as a well pump) or a small dedicated subpanel (such as
a Homeline or QO 6-12L100S) fed by the autotransformer output.
Does this help? Did I address your question?
Allan
Allan Sindelar
[email protected]
NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A
Certified B CorporationTM
3209
Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
On 3/19/2014 7:26 PM, Dave Click wrote:
Dan,
690.10(C) doesn't say no. It says that if you have a single 120V
inverter output connected directly for a 120/240 panel then you
can't put a 240V load in the panel-- in this case you'd either
have L connected to both phases of the panel or I guess you
could just use half the breakers in the panel. For a 240V load
it would just see 0 volts phase to phase, but for a multi-wire
branch circuit with current on both legs you'd potentially
overload your neutral conductor.
Now when you use either a 240V inverter (or two stacked 120s) or
an autotransformer between the inverter and the panel, 240V
loads are fine since you have two lines 180 degrees out of phase
and voila, 240V. 690.10(C) wouldn't apply to this situation
since your inverter(s) would be supplying 240V (not 120) to your
1P 3W panel.
DKC
On 2014/3/19, 20:40, Dan Fink wrote:
Esteemed Wrenches;
Can anyone here help me with some simple talking points
for clients installing off grid systems? 240 Well pumps hard
wired to panel breakers are common, but everybody (who has
even a chance of surviving up here in middle of nowhere way
off grid) NEEDS a 240v welder outlet in the garage/workshop.
But 690.10(C) says no.
Am I missing something obvious? What do I tell these
potential clients?
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org