I should have mentioned that our installation is not a metal roof either.
Ours is a flat foam roof with large tilt racked arrays of SunPower modules.



I've spoken with SMA tech support twice on this and got the idea that
either I have a real ground fault or that there is some sort of inductance
related problem that they don't necessary have a fix for yet.



Best, August



*From:* [email protected] [mailto:
[email protected]] *On Behalf Of *Jeff Irish
*Sent:* Tuesday, March 25, 2014 6:34 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof



August,



We're seeing multiple inverters with the same error, and not getting the
best of answers or support from SMA on fixing the problem so far.  And this
is not a metal roof; it's PanelClaw on EPDM.



Jeff Irish

Hudson Solar
------------------------------

*From:* [email protected] [
[email protected]] on behalf of August Goers [
[email protected]]
*Sent:* Tuesday, March 25, 2014 8:41 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof

Hi Marco,



Did you ever make any progress on this issue? We're having an interesting
issue with one of the new Sunny Tri-Power inverters (a 24 kW unit in this
case) where we get an error "residual current too high." We've only done a
little troubleshooting so far but I don't think we have a ground fault.



Best,



August



Luminalt



*From:* [email protected] [mailto:
[email protected]] *On Behalf Of *Marco Mangelsdorf
*Sent:* Friday, March 14, 2014 9:56 AM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof



Probably not.



*From:* [email protected] [
mailto:[email protected]<[email protected]>]
*On Behalf Of *RE Ellison
*Sent:* Friday, March 14, 2014 1:24 AM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof



Is the metal roof grounded? Just a fast thought.



bob



*From:* [email protected] [
mailto:[email protected]<[email protected]>]
*On Behalf Of *Marco Mangelsdorf
*Sent:* Thursday, March 13, 2014 10:31 PM
*To:* 'RE-wrenches'
*Subject:* [RE-wrenches] Unusual problem with SMA TL inverter on metal roof



Friends,



We have run across an odd technical problem at our commercial install at a
laundromat on our island.   Attached is the description of the issue from
SMA.  We don't know much except that we are switch out the TL inverters to
the old style US inverters because SMA has no fix for the phantom ground
tripping.  The issue is beyond our feeble understanding.



Any observations to share?



Thanks,



marco


------------------------------

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4336 / Virus Database: 3722/7186 - Release Date: 03/12/14
------------------------------

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4336 / Virus Database: 3722/7186 - Release Date: 03/12/14
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to