Actually the arc is normal,  It just depends on where in the waveform is when 
the DR switches between Inverter to Generator and how dark the room...

If the Relay is failing direct power, Inverter sales and Service in Tenn, and 
Phantom Power Services (Craig Wilburn) should have spare parts.

Another trick you do is power down the inverter... And disconnect all cables
Take the top cover off
If it's the older relay without a plastic cover on it you can actually visually 
inspect the relay contacts.   If the contacts are severely burned then to 
prolong life you can use fine grit paper to sand the connections... but this is 
the beginning of the end... You better start planning on a replacement at that 
time.


Feel free to send me a pic of the connections and I can tell you have bad they 
are...

________________________________
From: [email protected] 
[[email protected]] on behalf of Allan Sindelar 
[[email protected]]
Sent: Thursday, March 27, 2014 5:34 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Arcing from inside Trace DR2412

Benn,
I recently addressed a similar issue on this list in regard to an old SW4024 
that showed a visible arc when the generator was disconnected, and the general 
response was that the arcing didn't represent a failure, that it was fairly 
routine.

Ask him when he sees the spark. When the unit sees ac, it waits about 30 
seconds, latches and then ramps up to its maximum current setting. If it 
doesn't latch or ramp up a control or relay board is likely bad. The DR is 
repairable, and some shops, such as Inverter Service Co., a part of Direct 
Power in Albuquerque, can repair it, but with shipping it's not worth fixing 
unless it's all he can afford. The repair will cost more than a working DR is 
worth, but still likely less than any new replacement.

Certainly there are far better inverters available. But the fact that the 
customer has continued to use the DR suggests that (a) he is probably satisfied 
with it otherwise, and (b) is on a tight budget. Therefore my advice would be 
to make sure there's a breaker on the AC input (this won't prevent the arcing 
but will allow shutoff in case of failure, and set aside the money to replace 
the DR if it fails. It may last for years like this.
Allan

Allan Sindelar
[email protected]<mailto:[email protected]>
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com<http://www.positiveenergysolar.com/>

Steve Higgins
Technical Services Manager
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of
[cid:rolls62721f]<http://www.rollsbattery.com>



On 3/27/2014 4:36 PM, Benn Kilburn wrote:

Wrenches,
An off-gridded (system installed by others) called me yesterday with a concern.

His system is older and has had mods added over the years. It is up to 7x 
Siemens SP75 and 1x She'll SQ80P.

I believe the inverter is the original. It is a Trace DR2412, and where the 
concern stems from.
He says he has noticed an arc from inside the inverter about 3 of the last 8 
times he has fired up his generator (remote start next to inverter). He 
described seeing the arc thru the vent fins on the top right of the inverter.

Is this internal arc typical when a generator connects to the inverter and he 
just hasn't noticed it before?

...or is his ol Trace toast?

Thanks,
benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and 
typos.
_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>






This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious content.
The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited. %^^%

<<inline: rolls62721f>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to