Corey,

I'm not pro nor con one way other another on the use of the 1M resistor Chris 
mentioned in the system you described.

However .. if you DO end up following his suggestion .. there are precautions 
you'll need to observe:

1. Resistors have a maximum voltage rating.  Make sure the resistor you use is 
rated at least 2 kV to prevent arc-over or similar.  I'd recommend 5 kV.

2. Though 1 milliamp is a small amount of current, 1000V x 1 mA = 1W.  Use a 
resistor rated at least 2W.  I'd recommend a 5W.

There's more info we could exchange.  This is a start.


I wish we had a way to hold a big conference call to discuss the issues you're 
experiencing, along with several related items, including the somewhat 
rhetorical question Erika posed.

To her query .. unless the PV system is "bipolar" by design, the array 
[typically] can NOT be grounded on either leg when used with a transformerless 
inverter.

At a minimum, to ground one leg would defeat the ground-fault detection 
circuitry in the inverter and hopefully cause it not to operate.  Worst case, 
grounding one PV leg will open fuses, trip circuit breakers, and blow up 
transistors.  The operative word here: "typically".  There may be a strange 
topology out there that would be an exception .. but I'm not aware of any.


Dan



--------------------------------------------
On Fri, 3/28/14, Chris Mason <[email protected]> wrote:

Subject: Re: [RE-wrenches] Capacitive Discharge Test Results
To: "RE-wrenches" <[email protected]>
Date: Friday, March 28, 2014, 3:30 PM
 
If you are using a high resistance meter, you may be experiencing phantom 
voltages. Here's a Fluke paper on it.

http://support.fluke.com/find-sales/Download/Asset/2105317_A_w.pdf

You might also discuss with the manufacturer putting a 1M ohm resistor from the 
center of the strings to the grounded roof to bleed off any stray voltage. It 
would only bleed 1mA at 1000V so it would not affect performance. Usually this 
voltage is apparent when the strings have not connected to the load.



On Fri, Mar 28, 2014 at 3:41 PM, Corey Shalanski <[email protected]> 
wrote:

Fellow Wrenches,

We recently commissioned a 220kW rooftop PV system and are having some inverter 
malfunction issues. The system details are as follows:
    - Inverters: Power One Aurora Trio-27.6 (x7)
    - Modules: Stion STN-130 (x1690)
    - Array: Strings of 14-16 modules each, 8 strings per combiner, 1 combiner 
per MPPT input

It has been less than two months since we commissioned the system, and we have 
already seen five of the inverters malfunction. While troubleshooting these 
issues the inverter manufacturer had me measure positive-to-ground and 
negative-to-ground voltage readings. At the inverter level I measured 
instantaneous voltages of 100-200V before seeing a bleedoff; at the string 
level the voltages were 10-20V before bleedoff.

The inverter manufacturer is concerned with the magnitude (~200V) of this 
instantaneous voltage and also the delay in bleeding off to zero - after about 
five seconds the voltage level was still approximately 50V (but still 
dropping). The manufacturer is claiming that this residual voltage should drop 
to zero much more rapidly AND the presence of such a delayed bleedoff indicates 
significant "leakage" coming from the array.They are further claiming that this 
leakage is responsible for the damage to the inverters. They suggested using a 
megger to test insulation resistance throughout the installation.

My questions to the group:
    - Is there any truth in the inverter manufacturer's claims?
    - Do my field measurements seem out of range from what others are seeing 
with ungrounded arrays?

Thanks for any information you can provide.
--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to