Bill Brooks should probably respond to this also, but reading the NEC, it looks like if the wires do not go inside the building to run more than 5 feet (as the crow flies), the the rapid disconnect does not apply. OR, less than 10 feet from the array IF the PV is mounted on that building.

boB



On 4/18/2014 1:34 PM, Aaron Mandelkorn wrote:
The rapid shutdown language is so confusing. When looking at the rapid shutdown language, does PV 
systems "on" a building refer to only situations where the array is on a building; or 
does it include DC conductors as well. For example, if the DC conductors from a pole mounted array 
run up the side of a building before punching in to the inverter, does this require rapid shutdown? 
 Is this PV system considered "on" a building?