If NEMA 3R works, you can also consider a Soladeck combiner on pitched
roofs. They make one for combining up to three microinverter circuits on
the roof, and include circuit protection via DIN rail mounted breakers.

Jason Szumlanski

​Fafco Solar​



On Wed, Apr 23, 2014 at 11:11 AM, Drake <
[email protected]> wrote:

>  That would be a nice piece of hardware. Is there any reason you can't use
> a NEMA 3R panel?  They are used on roofs quite a bit, and are readily
> available.  The Square D, 8 space, outdoor box should work in most rooftop
> environments for the purpose you describe.
>
> At 06:18 PM 4/21/2014, you wrote:
>
> Hello Friends!
> Anyone have a lead for* NEMA 4x* stainless load centers (electrical
> panel)? Â Looking for 4 circuit version rated at about 60-100A @ 240VAC.
>
> Would like to use it for rooftop combiner for 3 Enphase inverter output
> circuits.
> Thank you!!
>
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified PV Installation Professional
> Renewable Energy Systems
> www.oregonsolarworks.com
> 541-218-0201
>
>
>