Kirk,

 

That is correct. Raceways are not rated for voltage. The key is whether the
conductor is intended to be installed in a raceway or not. Raceways are also
allowed to be used for physical protection only for direct buried cables and
exposed cables. The raceway is only required to prevent physical damage in
those applications. The conduit is chosen based on what level of physical
damage is expected. For instance, Rigid Metallic Conduit is generally used
above ground in parking structures because of the possibility of being
struck by a vehicle.

 

Bill.

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Kirk
Herander
Sent: Friday, May 16, 2014 1:43 PM
To: RE-wrenches
Subject: [RE-wrenches] 1000 volt conduit??

 

Hello,

Is there any specific conduit you'd recommend for 1000 volt arrays? I can't
find any reference of a voltage rating for EMT, ridged, PVC, etc. in the
code or spec sheets. Are these types OK to use? I assume its OK as long as
1000v rated wire is used. Am I correct? Thanks.

 

Kirk Herander

VT Solar, LLC 

Un-Common PV since 1991

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 



---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to