Kirk,
That is correct. Raceways are not rated for voltage. The key is whether the conductor is intended to be installed in a raceway or not. Raceways are also allowed to be used for physical protection only for direct buried cables and exposed cables. The raceway is only required to prevent physical damage in those applications. The conduit is chosen based on what level of physical damage is expected. For instance, Rigid Metallic Conduit is generally used above ground in parking structures because of the possibility of being struck by a vehicle. Bill. From: [email protected] [mailto:[email protected]] On Behalf Of Kirk Herander Sent: Friday, May 16, 2014 1:43 PM To: RE-wrenches Subject: [RE-wrenches] 1000 volt conduit?? Hello, Is there any specific conduit you'd recommend for 1000 volt arrays? I can't find any reference of a voltage rating for EMT, ridged, PVC, etc. in the code or spec sheets. Are these types OK to use? I assume its OK as long as 1000v rated wire is used. Am I correct? Thanks. Kirk Herander VT Solar, LLC Un-Common PV since 1991 www.vermontsolarnow.com dba Vermont Solar Engineering NABCEPTM Inaugural Certificant VT RE Incentive Program Partner 802.863.1202 --- This email is free from viruses and malware because avast! Antivirus protection is active. http://www.avast.com
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org