As an update- the system used at this install turned out to be a
currently-available product called SolAttach:
http://www.solattach.com/
On 2014/6/3, 11:11, Dave Click wrote:
Jason, thanks for the comment! I agree that systems could connect to
just sheathing and stay on the roof- I think Zilla has a product that
does this too. My concern about wind resistance stems from the fact
that there appeared to be an engineer's stamp on the Unirac calcs with
lag screws and then something completely different was installed in
the field. It's likely that this installer has used this same mounting
system in windier coastal areas so hopefully their fastener selection
had some informed analysis... I didn't see any, though.
And to be clear, I'm not looking to overrule another PE if it is in
fact an engineered system and it's just that the wrong set of plans
got submitted to the building department.
DKC
On 2014/6/3, 10:12, Jason Szumlanski wrote:
Dave,
I can't identify your hardware, but I just wanted to comment on your
comment about hitting rafters. There are products out there that can
obtain the requisite load ratings without connecting directly to
structural members. We have had systems engineered and permitted
using Ecofasten products on low-slope roofs that fasten only to wood
sheathing or metal roof materials in 170 mph zones in Florida (ASCE
7-10, FBC 2010). I'm not an engineer, but I've been told if there is
adequate data on pull-out and shear, you can use that data to
properly design a system without hitting rafters with the right
number of attachment points. I don't like the looks of what you
pictured, but it's plausible that it was an engineered system design.
The permit drawings not matching... that is another story...
If, for example, each of the six fasteners provide 100 pounds of
pullout strength with a safety factor, that would be good for 12 sq
ft at 50 spf uplift per attachment. 250 fasteners would be good for
about 5kW of solar.
Jason Szumlanski
Fafco Solar
On Tue, Jun 3, 2014 at 9:06 AM, Dave Click <[email protected]
<mailto:[email protected]>> wrote:
Hi all,
Anyone know what this racking system is? The permit drawings say
Unirac with lag screws and Eco-Fasten flashings, which this
pretty clearly isn't. I'd never seen this before, and I imagine
this wind resistance is not quite the 140 mph that the installer
claims it is. Of the ~250 wood screws holding this system down
into the roof, I think six of them accidentally hit rafters.
Thanks!
Dave
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org