Corey,

The line of reasoning is faulty. It's 705.12(D)(1). Micro-inverters are the exception because they are specially listed to share a breaker. As for the other inverters, doubling them up on a single breaker / disconnect probably goes against their installation instructions [110.3(B)] and it's unlikely that you could put multiple units on a single breaker anyway because when you take (2 inverters) x (rated current) x (1.25) you will probably come up with a minimum breaker size that is larger than the maximum allowed under the NRTL listing to UL 1741.

Dave



On 2014/6/26, 16:18, Corey Shalanski wrote:
We considered the necessity to shut down individual inverters and determined that the added costs of an inverter output combiner panel were not merited. I agree that in theory it seems beneficial to be able to switch each inverter individually, but how often does this occur in practice? For the relatively infrequent cases where we need to return to a jobsite and shut down an inverter - for troubleshooting/removal/etc. - we do not mind shutting down the other inverters (up to a limit) for what is hopefully a short period of time.

Again, this whole line of reasoning may be shown to be faulty if someone can directly point to the Code section that requires OCPD on each individual inverter.

--
Corey
?


On Thu, Jun 26, 2014 at 9:20 AM, <[email protected] <mailto:[email protected]>> wrote:


    Message: 5
    Date: Wed, 25 Jun 2014 19:17:57 -0700
    From: William Miller <[email protected]
    <mailto:[email protected]>>
    To: RE-wrenches <[email protected]
    <mailto:[email protected]>>
    Subject: Re: [RE-wrenches] Combining Multiple Inverters
    Message-ID: <[email protected]
    <mailto:[email protected]>>
    Content-Type: text/plain; charset="utf-8"

    Not allowed. You need a dedicated OCPD. Plus seems like a really
    bad idea.  How do you shut down just one inverter?



    Miller Solar



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to