The SPD will (or, should), "clamp" the input voltages, both positive and negative to ground at the MOV voltage rating during a lightning strike. The SPD 300 starts at about 500 volts on each leg of the SPD. The 600 SPD is higher voltage of course. Since, on the PV input side, the MOVs appear to be in series, an SPD 300 should clamp the plus and minus input to twice 500V or, about 100 volts which should not do anything to a charge controller operating up to 250 volts or even higher so I am not sire what happened here. We'll have to try to do an autopsy
on the controller if possible on this one.

We're still looking into the optimizer interaction issue. It doesn't really make any sense as to why they should "fight" though. We have talked with Tigo on this but nothing definitive
yet as to why.

Thanks and happy 4th of July,
boB



On 7/4/2014 7:51 AM, [email protected] wrote:
Anyone else having problems with Midnight Classics Flaming out (Literally)? We know they don't play nice with Tigo Optimizers. Wondering if a Midnight SPD might also look like a short to a classic when it clamps. only affected two of the four controllers. Two seemed to be un affected, one tripped off and reset, Not only did the last one let the smoke out, but went Dali in the process. Painted up the wall and everything.Suggestions? Thanks db

Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
NABCEP #092907-44


    -------- Original Message --------
    Subject: Re: [RE-wrenches] 2014 NEC
    From: Phil Forest <[email protected]
    <mailto:[email protected]>>
    Date: Tue, May 20, 2014 1:25 pm
    To: RE-wrenches <[email protected]
    <mailto:[email protected]>>

    Will,
    No problems with inspectors for us in MA, regarding rapid
    shutdown, since we recently switched to using SolarEdge central
    inverters with optimizer under each module, for roof mounted
    installs.
    So far so good. They seem well made and engineered. Tip: you have
    to enable the arc fault protection when commissioning, ships
    disabled.

    Phil Forest
    South Mountain Company

    On May 20, 2014, at 10:59 AM, Will White
    <[email protected] <mailto:[email protected]>>
    wrote:

    Wrenches,
Is anyone else having problems with inspectors and the 2014 NEC? In Mass we're having all kinds of issues with inspectors
    requiring/allowing an array of different things for 690.12 rapid
    shut down ranging from roof top disconnects, disconnects on the
    side of a house 20' up, disconnects in attics, or only
    disconnects that can be activated on the ground.  It varies
    between inspectors.
    We're also having problems with one inspector requiring arc fault
    breakers on Enphase even though there are no UL listed arc fault
    breakers that can be back fed or he wants us to run the trunk
    cable in a raceway.
    It's getting very difficult to install in Mass.
    Thanks,
    Will
    *Will White*
    Operations Manager - New England
    RGS Energy

    64 Main St. |Montpelier, VT 05602
    tel 802.223.7804 |mobile 802.234.3167 |fax 802.223.8980
    *RGSEnergy.com <http://www.rgsenergy.com/> **|
    [email protected] <mailto:[email protected]> *



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to