Hi Wrenches,

Happy post 4th!

My apologies if this has been covered ad-nauseum. But the 2011 NEC 690.16(A) 
and 690.16(B) sections continue to confuse many in the industry, including 
designers and equipment manufacturers.

The consensus on 690.16(A) seems to be that touch-safe fuse holders on all 
source circuits satisfy this requirement. My question is do the integrated 
plastic fuse-pullers (think SMA sunny boy) satisfy the requirement? For string 
inverters, I know Chint is replacing all their source circuit fuse holders with 
the touch-safe type while SMA and AE are sticking with the integrated fuse 
pullers.

2nd question:  690.16(B) seems to require a load-break disconnect at every 
combiner box to interrupt current flow. But what about on the re-combiner 
internal (or external) to a central inverter? Does a DC disconnect on the 
inverter side of the re-combiner fuses satisfy this? Many including SMA and AE 
are interpreting this as requiring an external DC disconnect on each circuit on 
the PV side of each re-combiner fuse. What do you think?

Thanks,

Jason M. Szrom, PE
Project Engineer
-----------------------------------
Gehrlicher Solar America Corp. - A Company of the M+W Group
21 Fadem Road, Springfield, NJ 07081
Phone 908-988-4459, Mobile 917-319-2517, Fax 908-219-4375
[email protected]<mailto:[email protected]>, 
www.gehrlichersolar.us<http://www.gehrlichersolar.us/>
-----------------------------------

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to