Insulated taps are for voltage.
L1 is forward, L2 backward, so as to measure total current in both legs
with one CT.




On Thu, Jul 10, 2014 at 4:39 PM, Corey Shalanski <
[email protected]> wrote:

> Wrenches,
>
> One of our customers has a utility meter CT cabinet ahead of his main
> disconnect - please see attached image.
>
> I have never seen this arrangement and would be interested if anyone can
> explain why the conductors are run in this fashion: I assume the insulated
> taps are for voltage reference purposes or to power the meter? I also
> assume the large donut is the CT? Are the conductors run criss-crossed due
> to they're being 180 out of phase?
>
> We are more particularly interested in the correct location to make a
> supply side interconnection in order to ensure that all PV energy is
> properly metered (our utility installs net meters in place of the
> customer's original meter). Assuming that our AHJ approves of an
> interconnection inside the CT cabinet, where would we splice into the
> service conductors: load side of the CT?
>
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
> ᐧ
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to