I recently needed to combine the output of two 20kw 3-phase inverters before 
the PV revenue meter. Instead of investing in an expensive panel for this, I 
ran each inverter output to its own 30A fused outdoor disco, then combined 
disco outputs in the meter socket using 2-pole replacement meter lugs (Milbank 
#K4977). A space and money saver for sure. And there is no panel for someone to 
come along later and install non system-related load circuits.

 

Kirk Herander

VT Solar, LLC 

Proven PV provider since 1991

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Mark Westbrock
Sent: Monday, July 14, 2014 8:41 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Combining Multiple Inverters

 

I agree that the exact placarding will depend on your AHJ, but you will 
certainly want one that says something like "This breaker panel is for 
combining solar inverter outputs.  Do not add any additional breakers or make 
any circuit connections".




----
Mark Westbrock
Field Manager & Employee-Owner

NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional

NABCEP Certified PV Technical Sales

 

 <http://positiveenergysolar.com/> Description: Image removed by sender.

 

Positive Energy, Inc.

510 S. Main St.

Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
[email protected] <mailto:[email protected]> 
www.positiveenergysolar.com

 

Description: Image removed by sender.

 

  <http://www.nabcep.org/installer-locator?state=NM> Description: Image removed 
by sender. <http://www.nabcep.org/installer-locator?state=NM>  Description: 
Image removed by sender.     
<http://www.solarreviews.com/installers/positive-energy-solar/> Description: 
Image removed by sender.    <http://www.bcorporation.net/> Description: Image 
removed by sender.

 

On Fri, Jul 11, 2014 at 3:45 PM, Jason Szumlanski <[email protected]> wrote:

I'd spring a few extra bucks for the QO line of panels. Better bus bar, better 
breakers, more common breakers (availability), etc.​

 

To answer your question, it depends on the interconnection method. Load side? 
Line side? Fusible disconnect or safety switch ahead of it? And some 
jurisdictions have their own opinion.​

 

On Thu, Jul 10, 2014 at 5:08 PM, Corey Shalanski <[email protected]> 
wrote:

Wrenches,

 

We have reevaluated our approach to combining multiple inverters and have 
settled on a SqD HOM612L100RB as a suitable solution - it is readily available 
from our local supply house for ~$25 and accommodates up to three full-size 
2-pole breakers.

 

What - if any - labels do you install on these panels: "AC (Solar) Combiner 
Panel"? 705.12(D)(4)? Other recommendations?

 

Thanks.

 

--

Corey Shalanski

Joule Energy

New Orleans, LA

Description: Image removed by sender.ᐧ

 

On Fri, Jun 27, 2014 at 12:41 PM, <[email protected]> 
wrote:


Message: 6
Date: Fri, 27 Jun 2014 12:41:52 -0400
From: Jason Szumlanski <[email protected]>
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Combining Multiple Inverters
Message-ID:
        <cajjtg3qzaxb-ugkkotupptd81ncnxv0uzid_frjfap5jo4f...@mail.gmail.com>
Content-Type: text/plain; charset="utf-8"

Dave,

I looked at the BR24L70RP a while back. It's really a 2-space, 4 cuircuit
panel. I think my conclusion was you actually need a single quadplex
breaker with common trip center and outer breakers to get (2) 2-pole
breaker functionality. The quadplex breakers come in a variety of mixed
rating (i.e. 15A center and 20A outer breakers). They are not readily
stocked and not cheap. We stuck with Sq D QO load centers for that reason.

Am I missing something?


Jason Szumlanski


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to