Situation: SMA5000TL with two strings of Rensola 260s was functioning perfectly 
fine.  We had to remove system for customer to repair roof after nasty hail 
storm (no damage to modules).  Reinstalled system and all commissioned fine.  
Week later - customer calls and says Arc Fault light is on.  Team goes and 
believes a not fully tight wire at fuse at roof-top Soladeck fuse holder not 
tight… resolved… no - one week later another call and same light.


Troubleshooting: take top module covering Soladeck roof enclosure off and check 
strings individually. We open the strings at the microfuse individually 
(ungrounded system, both positive and negative conductors are fused.)The string 
not on seems to have a small but present small voltage that quickly bleeds down 
to millivolt levels.  Check all connections, briefly think that the single 
removed module might be damaged but check Voc and Isc and check off as 
functional.  Two strings enter the DC disconnect separately and make 414 volts 
+/- a very small level.  But the A string bleeds off voltage approximately 
10-12 volts if the voltmeter is left on the terminals for 20-30 seconds instead 
of taking a quick, “point” reading.


Question:  what would cause this slow bleed and could this be why I don't see 
an arc fault light immediately but only have a few days?






Howard "Scot" Arey

Solar CenTex
254-300-1228

"Use the Texas Sun!"
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to