Hi Jay,
I had to deal with this once on a Trace SW
system. The cheapest option turned out to be to
just adding another inverter, not synchronized,
on the third leg of the generator.
All loads were 120/240, so no need for 208.
Commercial battery chargers were way expensive.
The non synchronized inverter charged batteries
just fine, and was used with a separate panel to
feed a few tough loads that could have caused the
lights to dim on surge. The three phase generator
windings were reasonably well balanced with this setup.
Drake
At 06:15 AM 7/24/2014, you wrote:
If the client does not need three phase but has
a three phase generator, you can rewire the
alternator to single phase, or have it done by a generator tech.
On Wed, Jul 23, 2014 at 10:35 PM, jay peltz
<<mailto:[email protected]>[email protected]> wrote:
Hi Guys,
Yes that could work, but then you wouldn't have
genny backup, which isn't a good idea IMHO.
I'm still researching if the client really needs 3 phase or not.
thanks all,
jay
On Jul 23, 2014, at 4:21 PM, Chris Mason wrote:
Are the loads three phase or just the generator?
On Wed, Jul 23, 2014 at 6:05 PM, Jerry Shafer
<<mailto:[email protected]>[email protected]> wrote:
Outback for sure but I have not seen the sw
line work on 3 ph nore the SI's I will say OB
work well. You may also want to consider a 3 ph
battery charger and a regular l120/240 battery system just a thought
On Jul 23, 2014 11:06 AM, "Jay Peltz"
<<mailto:[email protected]>[email protected]> wrote:
Hi all
I have a client who
Might need 3 phase battery based inverters for 208/120 US 60 hz.Â
I believe the choices are: Â SI, XW( with
reprogramming) and outback FX line.Â
This is not for motors, but running off of a 3 phase generator.Â
Anything I've missed?
Jay
Peltz power
PS thanks for all the comments as to my previous questions on batteries.Â
J
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org
--
Chris Mason
NABCEP Certified Solar PV Installer
Solar Design Engineer
Generac Generators Industrial technician
<http://www.cometenergysystems.com/>www.cometsolar.com
<tel:264.235.5670>264.235.5670
<tel:869.662.5670>869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org
--
Chris Mason
NABCEP Certified Solar PV Installer
Solar Design Engineer
Generac Generators Industrial technician
<http://www.cometenergysystems.com>www.cometsolar.com
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org