Friends:

 

I have checked out the Midnite purpose-made BOS cabinets for Sunny Island 
inverters.  My problem is they must be co-located with the inverters.  The OCPD 
needs to be closer to the batteries than this usually allows.  If your 
inverters are mounted on an interior wall with the batteries directly on the 
other side, these may work out OK because your battery leads will be short.

 

I forget if the Midnite panels have AC distribution.  I have divorced myself 
from using any sort of AC distribution built by RE manufacturers.  I am weary 
of making custom leads for QOU breakers and trying shoehorn too much into an 
FX1000,  Radian or Midnite BOS cabinet, for example.  We use only off-the-shelf 
load centers.  They are a good value due to economy of scale.  We provide one 
each for inverter fed, generator fed and mini-grid or grid fed, if present.  
Bypassing can be done easily with factory or custom made interlocks.  (I know 
custom made interlocks are not listed hardware but I can’t seem to find fault 
with such a simple device.)

 

See the following link for some details on how this can be done.  By the way, 
if you are transferring more than 100 amps you really need to use commercial 
grade panels.  We see the main lugs used as a house feeder but this has always 
bothered me.

 

http://www.millersolar.com/MillerSolar/Portfolio/Commercial/Red_Mountain/Red_Mountain.html

 

William Miller

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Mac Lewis
Sent: Monday, August 25, 2014 4:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island battery cable setup

 

Also see all of Midnite Solar products. The SMA epanels are functional but 
expensive. You may also like their battery combiner. Its good for 1000A DC.

Outback FX1000

William

Miller Solar

> On Aug 25, 2014, at 10:43 AM, Darren Anderson <[email protected]> wrote:
>
> Hi All ­ just wondering what products or general setup others are using to
> split the battery cables to two or more Sunny Islands?
> _________________________
> Darren Anderson | Project Manager
> Solar Electric Light Fund



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to