[Robin chiming in, below]

Dan, The 2014 690.12 is worded poorly. That is why there is so much confusion. MidNite Solar is sitting on the NEC2017 690.12 committee. There are a lot of smart people in this group. The 2017 version says ALL PV SYSTEMS, not just on or in buildings. The 10 foot space gets reduced to 1 foot like it always should have been.

There will be a lot of other clarifications too. The systems that use shunt trip breakers [with Remote Trip coil] and contactors are for string inverters. Shunt trip breakers will be used for battery based systems and grid tie inverters with an AC outlet like the SMA TL series. Micro inverters do not require anything like what our system is. They can use the existing backfed breaker in the main distribution box as long as it is labeled accordingly. Solar Edge has a system that meets the Rapid Shutdown requirement also.

The UL standard for Rapid Shutdown has been written. It is going to go out to a task force for review, comment and changes soon. MidNite Solar will be on that task force. The MidNite Birdhouse is going through UL now and is being evaluated to this new standard. All of our disconnecting combiners and SOBs are already ETL listed. UL is modifying the new Rapid Shutdown Draft standard as they come upon things in the Birdhouse that the standard didn't consider. One of the biggies that has not been sorted out is a requirement for feedback. Contactors, power supplies and a switch will meet the requirement for 2014. The issue with this type of system is that when you push the button to turn off the contactors, there is no way to tell that they actually opened up. Without feedback that verifies that the contactors are actually open, you are taking a chance with people's lives. 600VDC contactors can weld themselves closed. If first responders don't trust the Rapid Shutdown system, they are going to let the house burn. We do have feedback on the birdhouse system. Contactors do not have feedback. It is not simple to add this feature to a contactor based system.

Installing a switch 15 feet up on the side of a building or on the roof is not the intent of 690.12. This will not be allowed in 2017. The exact placement of the initiating device (Birdhouse) is not cast in concrete due to the differences in where main panel boards are located, but it will not allow things like mentioned here 15 feet up in the air or in the attic or on the roof.

Battery based systems are the most complicated to meet 690.12. The NEC committee is deferring a lot of this to MidNite as we are already doing it and have gone over all the different ways things can go wrong. We started designing our system right after the Bakersfield fire 5 years ago. The Bakersfield fire is what got the NEC to require disconnecting combiners. We couldn't imagine why a fire fighter would want to get up on the roof of a burning building to look for a combiner? This is why we started the birdhouse project way before anyone ever thought of the words Rapid Shutdown. Turns out this was a good thing since battery backed up systems make the issue ten times more complicated. We spent years working out issues and there were lots of them that required a start from scratch approach numerous times.

AC coupling to a battery based inverter does not automatically meet 690.12 as someone mentioned in this thread. That battery based inverter must also be shut off. The micro inverters would of course shut off when the utility is shut down, but the battery based inverters job is to keep things powered up when the grid is down. So the battery based inverter has to be shut down also.

It would also make sense to shut off an auto start generator with the Rapid Shutdown button. Some generators are designed to start up upon loss of grid. Once the first responders have the meter pulled, that could start up a generator and cause risk of shock. If the generator is designed to start on low battery, it could start a day later when the fire has been put out, but that also poses risk of electrical shock when unexpectedly the part of the house that is left all of a sudden comes live with juice.

The cost for a Rapid Shutdown system will vary a lot depending on what you want to shut down. You do not need to run conduit to all the boxes and switches. There is 600V Cat5e 90C USE-2 cable available that will suffice. I don't see a system being installed for less than $1500 though.

Robin Gudgels



On 8/27/2014 8:45 AM, Dan Fink wrote:
Hi Mac, all;
Since Colorado just adopted NEC2014 July 1, I have not heard any AHJ stories yet. But look at 690.12 (1): "Requirements for controlled conductors shall apply only to PV system conductors of more than 5 ft in length inside a building, OR more than 10 ft from a PV array."
(my emphasis on "OR")

I interpret this to mean that if a ground mount array is more than 10 ft from the building, then any PV circuits that run up the outside of the building from their trench (for example to penetrate the wall to the power center on the inside) must be controlled because they are "on" the building. And even if you penetrated right from the trench into the crawl space, then up to the power center on the inside wall, with less than 5 ft distance, still needs to be controlled if the array is more than 10 feet from the building because of that "OR"

The logic and safety advantage of this for firefighters is another topic entirely. As a first-arriving firefighter, I would spot the PV racks on the ground, walk over to them, and throw the disconnects on the nicely-labeled combiner boxes located within 10 feet of the array.

All thoughts appreciated, still puzzling this out.

Dan Fink
Buckville Energy
Otherpower
NABCEP / IREC / ISPQ accredited Continuing Education Providers
970.672.4342

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to