I've successfully operated isolated temporary installations where the 
ac-coupled inverter output significantly exceeds the battery-backup inverter 
nameplate rating. Obviously there has to be enough "firm" AC load to absorb at 
least the portion of the AC coupled output that exceeds the grid tie inverter 
capacity. 

Hypothetical example: 
(3) Power One 6 kW 240 output grid-tie inverters with 7.5 kW of PV modules 
each. 
(2) Schneider XW6048 battery backup inverters

Suppose the supported AC load consisted of a mix of refrigeration and other 
heavy loads with minimum demand during sunny hours of 6 kW. 
Or suppose the solar array consisted of modules on steep 45 degree East/West 
roof surfaces...

/wk


On Sep 14, 2014, at 8:55 AM, Tump <[email protected]> wrote:

All, I am wondering what the max AC Coupled back feed into an OBGTVX 3648 might 
be. I have installed a 4.9 STC array into a SMA TL5k inverter and the customer 
presently has an single OB GTVX with a T240 into a Eback up load panel. I would 
like to know if there are any limitations in this type of configuration using 
an AC coupling situation to operate during a grid failure.
Thoughts please.

> [email protected]               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to