Also 705.12(D)5 in 2011: (5) Suitable for Backfeed. Circuit breakers, if backfed, shall be suitable for such operation.
FPN: Circuit breakers that are marked "Line" and "Load" have been evaluated only in the direction marked. Circuit breakers without "Line" and "Load" have been evaluated in both directions. 705.12(D)4 in 2014: (4) Suitable for Backfeed. Circuit breakers, if backfed, shall be suitable for such operation. Informational Note: Fused disconnects, unless otherwise marked, are suitable for backfeeding. -Glenn From: RE-wrenches [mailto:[email protected]] On Behalf Of Allen Frishman Sent: Tuesday, September 16, 2014 5:48 PM To: [email protected] Subject: [RE-wrenches] QO Breakers ok for Back feeding? Wrenchers, One of my associates was asked by an inspector to prove that the QO breaker is rated for back-feeding. I seem to remember the code stating that as long as the breaker does not state that it is only rated for one direction then it is ok to back feed. Anyone have a reference to the code or literature from Square D that states it is ok to back feed? All feedback is appreciated. Al Frishman AeonSolar (917) 699-6641 <tel:%28917%29%20699-6641> - cell (888) 460-2867 <tel:%28888%29%20460-2867> www.aeonsolar.com <http://www.aeonsolar.com/>
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org