Bruce,
We routinely cut off DWV as suggested by earlier posts so that they are at 
least 1 inch below the surface of the back of the module.

To be clear these are sewage intake air vents and not exhaust vents for heating 
appliances. 

We do place a quarter inch wire cloth over the cut off vent and apply a four 
inch stainless steel hose clamp around the pipe just to prevent foreign objects 
from entering the vent pipe. 

I have never had an inspector question this method. 

With Regards
Carl Adams, President
SunRock Solar
513.290.9072 (cell)
513.766.6025 (office)

On Sep 24, 2014, at 1:37 PM, Ray Walters <[email protected]> wrote:

I agree with Kurt: you need a licensed       plumber in your area to advise 
you, if you're trying to keep the AHJs happy .
2nd,  I'm very sure you don't want an exhaust/ combustion type vent under the 
array.  I've had several over the years, and seen some arrays installed over 
them.  They can get fairly hot and put quite a bit of steam out.  I would not 
trust the module backing material to a concentrated long term dose; which 
module is going to have a problem first?   
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 9/24/2014 11:16 AM, Kurt Johnsen wrote:
> Should you decide to lower your plumbing vents I have found an inside pipe 
> cutter to be an inexpensive and handy tool. Cut the vent and lead off an inch 
> above your desired pipe height and use the inside cutter to cut the pvc pipe. 
> Go slow and be careful to keep air space between the pvc and lead as the lead 
> will cut very easily.
> 
>  
> 
> Also I wouldn't rely on us well intentioned wrenches to make the call on the 
> plumbing code in your jurisdiction. Though the state plumbing codes are 
> usually based on the international code, there will be differences. If you 
> can't pull up your state plumbing code online then ask your plumbing 
> inspector. In Florida the minimum height above a roof surface is 6" (904.1). 
> As for relocating 905.2 states that “all vent and branch vent pipes shall be 
> so graded and connected as to drain back to the drainage pipe by gravity”. 
> Table 710.1(1) shows that for 1.5” pipe a slope of ¼” per foot is sufficient 
> to handle 3 fixtures. I would take that to indicate ¼” / foot is plenty for a 
> 1.5” vent.
> 
> 
>> On Wed, Sep 24, 2014 at 11:20 AM, Dave Click <[email protected]> wrote:
>> Flipping through the '04 plumbing code I see a few slopes called out (1/4" 
>> per 1' for fixture vents, 1" per 1' for circuit vents, 1/2" per 1' for 
>> combination drain/vent...). Fixture vents have a maximum distance of a few 
>> feet from fixture trap to vent, but I don't think this prevents you from 
>> then running that vent horizontally. 916.2 states that for vents other than 
>> stack vents or vent stacks if your vent is >40' you need to upsize the whole 
>> vent pipe (tough to do for an existing building, of course). Stack vents 
>> have a "maximum developed length" of 100' for a 1.5" vent which should be 
>> enough space to get away from under the PV. I don't see any slope 
>> requirements specifically for stack vents but my non-plumber's eye may be 
>> missing something.
>> 
>> The stack vent sizing Table 916.1 appears (in part) here too and it looks 
>> like the tables match up to a 2.5":
>> http://www.engineeringtoolbox.com/drainage-vents-d_1110.html
>> 
>> DKC
>> 
>> 
>> 
>> 
>> On 2014/9/24 10:19, Jason Szumlanski wrote:
>>> I am unable to find anything in the Florida code that precludes covering a 
>>> plumbing vent. The code does require the vent to be 6" above the roof 
>>> surface I believe.
>>> 
>>> I was unable to determine if these vents need to be vertical with no bends 
>>> in the attic. Obviously you wouldn't want to create a trap in the attic, 
>>> but a couple of 45's to relocate a plumbing vent to accommodate more PV 
>>> seems like a desirable thing to do sometimes. Does anyone know if these can 
>>> be relocated, i.e. to an adjacent roof surface?
>>> 
>>> On my own home I had a vent to deal with. I broke out my saws-all, split 
>>> the lead like a banana and peeled it back, cut the pipe at an angle, and 
>>> folded the lead back into the pipe after applying sealant between the lead 
>>> and pipe. There is a 1" gap between the rim of the pipe and the back of the 
>>> module. My theory on this                           working safely is that, 
>>> a) there will be far less rainwater falling in and around this pipe with a 
>>> module over it, and b) it is about 24" from the roof ridge and there is a 
>>> module over it so there will be very little water sheeting                  
>>>          down from above the vent. Code notwithstanding, I felt this was a 
>>> solid                           method on my own home, and I have inspected 
>>> it after 6 months of Florida downpours and found no issues.
>>> 
>>> 
>>> Jason Szumlanski
>>> Fafco Solar 
>>> 
>>> 
>>> On Wed, Sep 24, 2014 at 6:38 AM, Bill Loesch <[email protected]> 
>>> wrote:
>>>> 
>>>> Bruce, August, et al,
>>>> 
>>>> This is but one more example of confusing terminology. A plumbing vent is 
>>>> not an exhaust vent!
>>>> 
>>>> A plumbing vent (what August calls a cold vent) is provided to allow the 
>>>> sanitary drain traps (and perhaps more) to operate properly. Without the 
>>>> properly functioning traps you would have sewer gas smell and sewer gas 
>>>> from the plumbing fixtures. This was commonplace when indoor plumbing was 
>>>> introduced to early adopters.
>>>> 
>>>> An exhaust vent is another animal entirely. An exhaust vent carries the 
>>>> combustion products to a suitable exterior location for dilution with 
>>>> ambient air. With the advent of power vented combustion appliances, a 
>>>> direct vent (one that takes in combustion air from the outside and 
>>>> naturally exhausts combustion products to the outside) is IMHO the only 
>>>> responsible way to install any power vented appliance in a freezing 
>>>> climate. (Power vented appliances come in both condensing and 
>>>> non-condensing flavors-they can penetrate the side wall or the roof). 
>>>> Originally, two separate pipes (with two independent properly separated 
>>>> penetrations) was used. That technique is still often used today. More 
>>>> recently concentric vents have been introduced both for condensing and 
>>>> non-condensing applications. A concentric vent can simplify some 
>>>> installations by putting the exhaust pipe inside a larger air intake pipe 
>>>> allowing for one, albeit larger, penetration. As you might imagine if the 
>>>> exhaust flow is hindered/diverted/redirected by an inappropriately located 
>>>> solar module combustion gasses will be re-ingested into the intake air. 
>>>> Not good for equipment performance. My understanding is the power vented 
>>>> appliance manufacturer dictates what kind of separation/clearances are 
>>>> needed with their product. My guess is you find they want at least a foot 
>>>> of separation between the top of the " inverted cone" and the module. 
>>>> Probably not what you had in mind for an aesthetically pleasing 
>>>> installation.
>>>> 
>>>> I hope this helps,
>>>> Bill Loesch
>>>> Solar 1 - Saint Louis Solar
>>>> 314 631 1094
>>>> On 23-Sep-14 6:54 PM, August                                     Goers 
>>>> wrote:
>>>>> Bruce and All,
>>>>> 
>>>>> Sorry, I hit send before I had a chance to complete my thoughts. What I
>>>>> meant to say was that I've found AHJs often allow us to cover cold
>>>>> plumbing vents but I've never tried or had any luck with covering hot
>>>>> vents including condensing boiler PVC vents. Once again, if in doubt you
>>>>> could see what the plan checker or inspector thinks.
>>>>> 
>>>>> Best,
>>>>> 
>>>>> August
>>>>> 
>>>>> -----Original Message-----
>>>>> From: August Goers [mailto:[email protected]]
>>>>> Sent: Tuesday, September 23, 2014 4:15 PM
>>>>> To: 'RE-wrenches'
>>>>> Subject: RE: [RE-wrenches] Modules over vents
>>>>> 
>>>>> Bruce,
>>>>> 
>>>>> I'll send you the CA plumbing code vent section offlist (attachment too
>>>>> large for this list). The way I read the code is that you technically
>>>>> can't cover any type of plumbing or hot vent. However, and I've run into
>>>>> little resistance from AHJs in the Bay Area by covering these. You might
>>>>> want to check in with your plan checker.
>>>>> 
>>>>> Best,
>>>>> 
>>>>> August
>>>>> 
>>>>> Luminalt
>>>>> 
>>>>> -----Original Message-----
>>>>> From: RE-wrenches [mailto:[email protected]] On
>>>>> Behalf Of Bruce Leininger
>>>>> Sent: Tuesday, September 23, 2014 3:49 PM
>>>>> To: RE-wrenches
>>>>> Subject: [RE-wrenches] Modules over vents
>>>>> 
>>>>> Hi all.  We're designing a system on a roof that is literally infested
>>>>> with plumbing, exhaust and combustion vents.  The combustion vents are PVC
>>>>> and none of the vents are more than 1.5' above the roof.
>>>>> 
>>>>> A racking company says that we can cover them with modules, since the
>>>>> modules will be at least 4' above the roof.  They have not yet provided
>>>>> any building code references to say that this is ok.  Do any of you know
>>>>> if the building code allows this?
>>>>> 
>>>>> Thanks.
>>>>> 
>>>>> Bruce
>>> 
>>> 
>>> 
>>>  _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to