The first gen of TL's did have a somewhat tight window for the DC window.

However, the new SBxxxxTL-US-22 (3kW - 7700kW, with secure power supply) Start 
Voltage is 125, MPPT is 175-480 (max of 600Vdc)

Also, for larger needs, the STP (12kW - 24kW)  start voltage is 150, MPPT is 
300-800V (max of 1000Vdc).

SMA America, LLC
Steve Jefferson
Service Line Supervisor
3925 Atherton Ave
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 3185 (direct)
Fax: +1 916 625 0871
Mobile: +1 916 622 4253
Email: [email protected]<mailto:[email protected]>
www.SMA-America.com<http://www.sma-america.com/>

[cid:[email protected]]<http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be>

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.


From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Mark Byington
Sent: Tuesday, October 07, 2014 6:59 AM
To: [email protected]
Subject: Re: [RE-wrenches] TL Inverters


Just a word of caution to those not having experience with SMA TL inverters - 
the larger units (7-11 kW) have an extremely narrow input DC voltage window.  
Depending on your module voltage and string design, all you need is a module or 
two to be shaded to fall out of the MPPT input voltage range.  The smaller 
units (3-5 kW) with the Secure Power Supply don't have this problem.  We no 
longer use these larger SMA TL inverters unless we can do maximum string length 
(e.g. strings of 8 for SunPower 96-cell) and there is zero shade at the site.

I believe SMA is in the process of adding larger units to the line that has the 
Secure Power Supply.  They added the 6 kW unit earlier this year, and just 
announced the 7 kW unit with Secure Power Supply.

Mark Byington
Cobalt Power Systems, Inc.



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to