Bob-O, Peter, Garrison,

        I appreciate the responses, will proceed accordingly.  I have seen some 
references to minimum distance to floor in some manuals.  Thank you,

Bill
Feather River Solar Electric

  ----- Original Message ----- 
  From: Garrison Riegel 
  To: 'RE-wrenches' 
  Sent: Wednesday, October 22, 2014 11:11 AM
  Subject: Re: [RE-wrenches] Mounting height


  Bill,

   

  See 2011 NEC 690.14(D) or 2014 NEC 690.15(A) Utility-Interactive Inverters 
Mounted in Not Readily Accessible Locations.  Basically there is no maximum 
height restriction for inverters but there are a number of requirements for AC 
and DC disconnecting means.  See NEC 404.8 for maximum disconnect height of 6’ 
7”…although exception No. 2 may allow the disconnect to be accessible by 
portable means.  I don’t know of any minimum height requirements in the code, 
although most (all?) string and microinverter manufacturers specify a required 
clearance below the inverter.  I suppose that would be the minimum. 

   

  Garrison   

   

  Garrison Riegel

  Project Manager | Solar Service Inc

  [p] 847-677-0950 | [email protected]

   

  NABCEP Certified PV Installation Professional™

   

   

  From: RE-wrenches [mailto:[email protected]] On 
Behalf Of frenergy
  Sent: Tuesday, October 21, 2014 11:02 PM
  To: RE-wrenches
  Subject: [RE-wrenches] Mounting height

   

  Wrenches,

   

          I can't seem to find a reference to the heights allowable for 
inverter installs, either minimum or maximum (need both).  For that matter, AC 
combiners, DC discos, any switchgear related to the inverter(s).

   

          Any help appreciated.

   

  Bill

  Feather River Solar Electric

  solar powered since 1982



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: [email protected]

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to