The inverter to generator ratio is entirely the designer's call and comes into play for large generators (for residential systems as mentioned in earlier replies, it's a bad idea).

Interconnecting in spot networks in dense urban areas has a similar issue in that the distribution system can't handle backfeed. In downtown Boston a few years ago I believe that the max PV that could be interconnected was something like 1/10 or 1/15 of the demonstrated MINIMUM demand for that building over the previous year-- just to make absolute sure that there wasn't a chance of backfeed. Other solutions include things like reverse power relays such that if the PV system does start backfeeding the system, the relay would trip the inverter offline.

Of course any time you're interconnecting on the load side, you of course take responsibility for anything bad that happens with the generator. This should lead to an extremely conservative ratio being used and regular monitoring to verify that the PV never comes close to backfeeding something it shouldn't. Also, any issues with power quality (real or perceived) can complicate your project substantially, thinking of William's recent issues with the UPS and Sunny Islands. I wonder if this could complicate a generator warranty, too, unless you were somehow able to get the manufacturer's blessing ahead of time.

Another comment I remember from an earlier Wrench conversation was that inverter contributions on the load side of a generator won't proportionally drop fuel consumption-- that is, if your generator's load is 500kW and your PV is putting out 250kW, you're not going to have a 50% reduction in fuel use. So it takes some equipment-specific analysis to figure out what exactly your customer's savings would be.

DKC



On 2014/10/28 12:35, Phil Forest wrote:
Interconnecting the inverter output to the utility side of the transfer switch 
is not necessarily an absolute rule. A knowledgeable solar EE told me a few 
years back, that interconnection can be made on the load side if the inverter 
kW output is small compared to the generator kW, that large kW generators can 
produce clean AC power allowing the inverter to operate and to operate without 
risk of burning out the generator.  I don't remember what the inverter to 
generator ratio needs to be, or if other criteria needs to be met.
Never tried it, we always connect to the utility side.

Phil Forest
South Mountain Company

On Oct 28, 2014, at 10:48 AM, Corey Shalanski <cshalan...@joule-energy.com> 
wrote:

Wrenches,

We frequently encounter residences with backup generators. The question that 
arises: how should the PV system be interconnected?

I have searched the archives and found some good information about this subject, but 
nothing definitive. I have fallen into the habit of broadly proclaiming that the PV 
system *must* be interconnected on the "utility" side of the transfer switch - 
in order to prevent backfeeding into the generator and thereby eliminate unintentional 
equipment damage. Is this concern justified? If so, should this be an absolute rule or 
would it depend on the generator make/model?

Thanks for any insights.

--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to