Hi Daniel,
I typically vent them the way you do, which will allow any small
amount of hydrogen out. The customer is absolutely adamant about
venting these to the outside. I will cooperate so long as his method
doesn't compromise the system through cooling the batteries
unnecessarily in the dead of winter.
He is a lawyer and came to the conclusion of the need for venting to
the outside from reading the NEC which says that sealed batteries
"require the same amount of ventilation" as liquid lead acid
batteries. The code also says to vent appropriate to battery
technology, so the code says two conflicting things. On the other
hand, it doesn't say that liquid electrolyte batteries need to be
vented to the outside. They will sure stink if you vent them to the inside.
Drake
At 09:54 AM 10/29/2014, you wrote:
I just re-read the original post Drake. These are AGM batteries. Do you have
a "belt, suspenders,...then a rocket pack" type of client here?
We typically vent our AGM boxes with small louver vents top and bottom to
allow the batteries to ventilate for cooling purposes, not H2 concerns.
With Regards,
Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13
-----Original Message-----
From: RE-wrenches [mailto:[email protected]] On
Behalf Of Ray Walters
Sent: Tuesday, October 28, 2014 11:12 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Passive Battery Venting
That's why we usually have the batteries in a garage, basement, or out
building that is not open to the living space.
I've seen some cases of very well sealed and insulated enclosures allowing
batteries to over heat, and also build up a lot of acid damaged connections.
Boxes I've seen with more air space and less sealing don't get this build
up, but you're correct: they do occasionally allow H2S into the surrounding
area.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 10/28/2014 8:10 PM, Jerry Shafer wrote:
>
> We do what we can to seal the enclosure so if or when a battery fails
> and really gasses off the two vents on the same wall regardless of
> wind direction will vent the gas. If it is not sealed then the gas can
> travel through out the area this is not advised.
>
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2247 / Virus Database: 4031/7973 - Release Date: 10/29/14
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2247 / Virus Database: 4031/7973 - Release Date: 10/29/14
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org