Nick:

 

We have structural engineers we work with on a regular basis, but we have never 
had to engage one in this particular capacity.  On this particular job there 
are two things unique:

 

1.    We are being asked to document the truss construction but not being asked 
to have any structural analysis performed on the truss.  I don’t believe a 
building official will be performing the calculations, so why bother?  (We have 
argued that the PV equipment is allowed to use the capacity reserved for “live 
loads,” obviating the need for engineering.  This is generally described as 
three pounds per square foot.)

 

2.    We have never been required to get an engineer’s stamped approval to 
attach lags to a truss member.  I am fully aware that it is quite possible to 
do this job incorrectly.  The lag must be sized so as not to split the wood and 
it must be applied near the middle of the truss member.  Again, no structural 
analysis is being required, so up-lift is not an issue, therefore lag size is 
not an issue.  I think it a bad precedent that solar contractors be required to 
hire an engineer every time they drive a screw.  California passed and adopted 
AB2188 that promotes streamlined permitting.  In the draft guide book are 
guidelines for proper lag application, specifying where on the width of a truss 
member a lag could be driven.  I think it much more sensible if a building 
jurisdiction require that a protocol be established for proper workmanship 
rather than require the added expense of having an engineer approve every 
fastener.  The jurisdiction is absolutely correct in their citation and 
application of the building code – it does say an engineer must approve any 
modification, including drilling -but this added expense for engineering does 
not seem sensible.

 

I am looking for any help from the members of this list-serve for strategies 
for negotiating with the building officials reviewing this permit application.  
I have presented documentation from the proposed AB2188 guide book.  The 
legislation does not apply until September of 2015, but we have used the same 
strategy when citing pending code changes to some success.  Any other ideas are 
welcomed.

 

Sincerely,

 

William Miller

 

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Nick Vida
Sent: Friday, November 21, 2014 8:52 PM
To: wrenches
Subject: [RE-wrenches] Tile Roof mount compliance

 

Hi William,

 

We deal with this all day in California. You should go in the attic, figure out 
the truss type (howe, scissor...), get the spans and sizes of the wood, and 
pictures of the grade stamps. You can then send this off to a structural 
engineer to get a letter and a digitally stamped set of your plan set. The 
Engineer may request structural additions, or different spacing for the 
penetrations, but most truss is pretty sturdy and capable of supporting the 
solar panels. 

 

If you throw a rock on linkedin, you will hit a Structural Engineer. If you 
need some help, send me a note off list.

 

Nick Vida

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to