Wayne,
I don't think that you are correct. The bus rating of a 200A
service panel may or may not be 200A, but it's not simply 120% of
the panel's rating.
The original 120% rule was premised on the fact that in
residential applications, panelboards (and thus busbars) were
seldom if ever run at full ampacity, and thus a 20% "negative
load" of a PV system was unlikely to ever cause overloading and
overheating of the busbar. You'll note that this was originally
allowed only in residential applications; commercial buildings
were expected to likely run at or near capacity.
I think you'll need to get the actual busbar rating from the
manufacturer.
Allan
Allan Sindelar
[email protected]
NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy,
Inc.
505 780-2738 cell
On 11/30/2014 4:45 PM, Wayne Irwin wrote:
Hello Wrenches,
Hope you all had a nice Thanksgiving.
I have an AHJ asking for the service panel buss rating and the
service panel buss protection rating.
Am I correct to assume that the rating is the service panels
designated rating x 1.2% (ie 200A x 1.2 = 240)?
and that the buss protection is the combined input breakers?
200 Main breaker + 40A solar back feed = 240A?
Given that
there are many different size panels (150A and 200A) that
share the same bus, I have a difficult time believing this
to be true.
If there is any designated signage or data sheets
specific to the service panel, where might I find this?
I have looked at Schnider but have not been able to find
anything specific.
Thanks,
Wayne
Irwin,
President
License
#CVC56695
State
Licensed Solar Contractor
Pure
Energy Solar International Inc.
[email protected]
http://PureEnergySolar.com
http://SolarChargingStation.net
352
377-6527 Office
352
336-3299 Fax
352
316-1637 Cell
The Sun Is
Always Shining!
The
content of this message is Pure Energy Solar Confidential.
If you are not the intended
recipient and have received this message in error, any use
or distribution is
prohibited. Please notify me immediately by reply e-mail and
delete this
message from your computer system. Thank you.
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org