Yes, running on gen set was the first thing we tried. Breakers were off on all units initially. The first unit we lit tripped out on some random error, but the other two lit up fine. After a few min of breaker off, the first one tried to light up, but the genny couldn't handle all three at once (80's vintage 5k propane Onan -- the most we could get out of it without pulling the voltage out of spec was 10A @240vac).
We switched back over to the RE system and everything ran just fine. We measured 14aac at full draw. That's when we discovered the units all run properly (on RE) if you either leave them on all the time with the temp turned down or briefly turn them off (with the remote controller) for a short time. Not sure, but it looks like somewhere around 4 hours of off from the controller is when the comm/relight problem happens. Mitsubishi is now talking about using a different controller to reduce the standby draw (So they can stay on all the time), but it sounds like they'd still like to blame the RE system. I'm still thinking bad sushi.
db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44
-------- Original Message --------
Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback
VFX Off Grid
From: jay peltz <[email protected]>
Date: Sun, November 30, 2014 8:12 pm
To: RE-wrenches <[email protected]>
HI Dan,Have you tried this on a different power source, say generator etc?You might also try a different inverter brand just to make sure.I once had radio noise from a magnum, some years ago. Tried everything, in the end, I swapped it for a VFX and the problem was gone, customer was happy.And I'm going to agree with Mitsubishi, most likely the inverter.The OB/FX just isn't compatible with some machines.jaypeltz powerOn Nov 30, 2014, at 4:29 PM, <[email protected]> <[email protected]> wrote:_______________________________________________We're still not at the bottom of it. Seems Mitsubishi is doing their level best to finger the RE system. Yes, the current wave form (On a Fluke 43 Power Analyzer) has a shoulder.. looks down right funky on one inverter thru the X240 until the 2nd inverter lights. Current also looks funkular when each mini split is lit (Pulses).. Still, I'm thinking it's more about how the mini splits toke power rather than how the Outbacks produce power. The voltage waveforms look fine.the other chin scratcher is that it seems this model of mini split has only been around since spring. There might be a model specific cold weather setup the AC folks missed. Something about a jumper on a control board that needs to be snipped to enable the compressor heater.We also noticed that all mini splits work just fine if you leave them on and turned down.. But that kind of power draw for folks that have been loving off grid since 92 is just unacceptable. (these guys were turning off GFI breakers because they could see a draw).Either way, the power system itself is working fine as is everything else in the house. And no, the new power system has not kept the lawn mower from starting or the dog from eating the cats food.Peace. dbDan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44<sigimg0.png>-------- Original Message --------
Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback
VFX Off Grid
From: Wayne Irwin <[email protected]>
Date: Tue, October 21, 2014 8:52 pm
To: Wrenches <[email protected]>
We have found that the mini-splits have only had issues while gen sets are running.
In some cases (when on genset) the mini's will run irregularly or flash a fault status.
Rather than try to have the mini's run on gen power we install dc chargers to charge batts from gen power.
My thought is that the AC Installer either has something wrong or the Mitsubishi's have very tight parameters.
Be sure that the wiring from the inside unit to the outside unit are correct. Should be only three wires (plus gnd). Very easy to check.
Possible alternative solution would be look into the cost of installing a Gree since they are the least expensive.
Wayne Irwin,
President
License #CVC56695
State Licensed Solar Contractor
Pure Energy Solar International Inc.
[email protected]
http://PureEnergySolar.com
http://SolarChargingStation.net
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
The Sun Is Always Shining!The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your computer system. Thank you.
Date: Tue, 21 Oct 2014 11:23:31 -0600
From: [email protected]
To: [email protected]
Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback VFX Off Grid
The Outback is not a perfect Sinewave. It still has tiny steps in the wave, and when electronics have a problem, its usually with the wave form as it crosses zero voltage . Instead of being instantaneous, it has a few milliseconds of time the wave is at the zero crossing, which can drive some electronics nuts. I don't understand the issue beyond that, but apparently the electronics use the zero crossing for timers and synchronizing, and they're looking for an instant "click", not a smear.
Do the heat pumps work with the generator? Even though generators can have more harmonic distortion, they do usually have a clean zero crossing.
If this is the case, I'm afraid I don't have a cure. We used to use capacitors, but Dan from Exeltech just poo pooed that fix in another recent thread, so I don't have any other tricks up my sleeve.
R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760On 10/21/2014 8:54 AM, [email protected] wrote:
Anyone else had issues with Mitsubishi Mini Split heat pumps fighting with Outback VFX off grid inverters? Everything is brand new. Outback VFX7248, three separate heat pumps. The heat pumps shut down reporting multiple / confusing input commands. The heat pump guys want to blame the power system. I'm thinking bad Sushi. Thanks db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44<ATT00001.png>
_______________________________________________ List sponsored by Redwood AllianceList Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org