Keep and eye on the batteries... when they allow this far of a discharge and go 
into cell reversal often they are much weaker than the rest of the batteries.   
I would have the customer cycle them once or twice a week to the 85-90% SOC, 
just to test how healthy the battery bank is.

To do so, disconnect the AC input to the inverter and let the inverter power 
some loads until the Magnum says they are 10-15% down... Then reconnect the AC 
input.   I would do this for 4 weeks.

After about a month,get them charged up to what you think is full then do a 
load test, find out what the C/10 discharge rate is and apply that amount of DC 
current load,  you should get that amount of current for at least 5 hours 
before the voltage drops below 2.0 volt per cell. (50%) state of charge.     
Measure each battery every 1/2 an hour with a volt meter... battery voltage 
shouldn't drop near (assuming 12v cells) 12 volts for at least 3.5 to 4 hours.

You will need a current meter to monitor the amount of current you're drawing 
from the battery.

Variance can be +/- 10 to 15% depending on the type of loads you place on the 
battery bank, this is why it's nice to have a linear load tester...  Good ones 
run about $15-20K...

My guess is you have a couple of failed, or weak cells, that are aggravating 
the overall issue.

Hope this helps...

________________________________
From: RE-wrenches [[email protected]] on behalf of RE 
Ellison [[email protected]]
Sent: Friday, December 19, 2014 7:16 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum System - Discharged Battery Bank

First time I ever saw one of the bank of 80 cells are just about put me in a 
panic

Had no idea they could do that either


Bob Ellison


Steve Higgins
Technical Services Manager
P: +1.902.597.4020
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of
[cid:rolls7dbc5a]<http://www.rollsbattery.com>

On Dec 19, 2014, at 9:48 AM, Corey Shalanski 
<[email protected]<mailto:[email protected]>> wrote:

Update on my investigation:
I visited the customer's house yesterday to set up a pulse charger. Much to my 
surprise the three batteries that originally registered negative voltage are 
now reading positive. Does this make sense - are batteries able to shift 
between negative and positive voltages at such a low charge level?

I do not see any evidence of distorted cases.


On Thu, Dec 18, 2014 at 7:58 AM, <[email protected]<mailto:[email protected]>> wrote:

I second tump.
Most likely a bad /cell battery took out the system.
As these are VRLA batteries, I'm curious do,the cases look damaged such as 
expanded or sunk in?

Jay
Peltz power
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



This email and its attachments have been scanned by mailWatch E-Mail Firewall 
for viruses, spam, and malicious content.

The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to